PSS/E Based Network Frequency Response Analysis Tool Yu (Terry) Tian, MSc student, [email protected] Department of Electrical and Computer Engineering, University of Alberta Motivation Software Algorithm Left figure shows IEEE 14 bus system. A shunt capacitor bank is to be installed at bus 13 to support voltage and to improve power factor. The following two options are analyzed through a frequency scan study at bus 13: Software Features Software Graphical User Interface (GUI) Transformer = + ℎ Transformer tap ratio and phase shift in three sequence are also included in the model. Transmission Line PI Model = + ℎ =×ℎ Distributed Line Model Long line effect is considered. Passive Load Series Impedance Model CIGRE Model Shunt Element = = × ℎ ℎ = ÷ ℎ ℎ Generator = + ℎ + = 2 = + ℎ 1 = 2 / = 1 = 0.073ℎ 1 = 1 6.7 − 0.74 Nov. 06, 2013 IEEE 14 Bus System Diagram Frequency Scan GUI Switching Transient Simulation GUI PSSE Network Frequency Response Tool ETAP CYME Our Tool Case File ETAP case CYME case PSSE case Frequency Scan Positive-Sequence Impedance Zero-Sequence Impedance × × Driving Point Impedance Transfer Impedance × × Harmonic Calculation Spectrum / Waveform Output Comply IEEE 519 Standard × Capacitor Loading per IEEE 18 × A Python software package developed by PDS-Lab which analyzes network frequency response on the selected PSS/E case file. Since the PSS/E itself does not have harmonic analysis functions, this software can be treated as an 'add-on' of PSS/E. Typical applications of this software include: Identify Resonance Filter Design Verify Standards/Limits Compliance Harmonic Problem Troubleshooting Equipment Sizing Equipment Loading Assessment Interact with PSSE directly Support up to 50000 buses User friendly interface Reliable validated result Highly customizable Easy install/uninstall Read PSSE Case File Retrieve steady state bus voltage V(0) from PSS/E Modify PSSE case for each frequency Apply a fault at bus i, Bus voltages after the fault (Vi and Vj), and fault current at bus i (Ii) are retrieved from PSS/E fault analysis result. Driving point impedance: Transfer impedance: = (0) = (0) Option 1 Option 2 Add 2 Mvar capacitor bank at bus 13 Add 1.8 Mvar capacitor bank at bus 13 Very high impedance at 19 th harmonic, not good Lower impedance at 19 th harmonic, better than option 1 Software Demo Frequency scan result at bus 13 Frequency scan result at bus 13 Resonance: Because of the existence of both inductive and capacitive components in the system, at certain frequencies, resonance conditions might occur at some buses. If the resonance occurs at a bus where a harmonic current is injected into the system, an overvoltage will be observed. Frequency Scan: A frequency scan is a plot of the driving-point / transfer impedance at a system bus versus frequency. The bus of interest is one where a harmonic source exists. The frequency scan is a very effective tool to detect resonances which appear as peaks (parallel resonance) and valleys (series resonance) in the plot of impedance magnitude vs. frequency. One of the most common ways to obtain the harmonic impedance is by using EMTP software. This requires a significant manual labour to collect a huge amount of information and to model a usually large interconnected network. Hence it is desirable to have a software that can run frequency scan directly on a PSSE case file, which stores all the system information and is well maintained by utility companies.

Upload: phamphuc

Post on 04-May-2018

237 views

Category:

Documents


4 download

TRANSCRIPT

Page 1: PSS/E Based Network Frequency Response Analysis Toolapic/uploads/Forum/poster15.pdf · PSS/E Based Network Frequency Response Analysis Tool Yu (Terry) Tian, MSc student, tian7@ualberta.ca

PSS/E Based Network Frequency

Response Analysis Tool Yu (Terry) Tian, MSc student, [email protected]

Department of Electrical and Computer Engineering, University of Alberta

Motivation Software Algorithm

Left figure shows IEEE 14 bus

system. A shunt capacitor bank

is to be installed at bus 13 to

support voltage and to improve

power factor. The following two

options are analyzed through a

frequency scan study at bus 13:

Software Features

Software Graphical User Interface (GUI)

Transformer

𝑍𝑇 ℎ = 𝑅𝑇 + 𝑗ℎ𝑋𝑇

Transformer tap ratio and phase

shift in three sequence are also

included in the model.

Transmission Line

PI Model

𝑍 ℎ = 𝑅 + 𝑗ℎ𝑋

𝐵 ℎ = 𝐵 × ℎ

Distributed Line Model

Long line effect is considered.

Passive Load

Series Impedance Model

CIGRE Model

Shunt Element

𝐺 ℎ = 𝐺

𝐵 ℎ = 𝐵 × ℎ 𝑐𝑎𝑝𝑎𝑐𝑖𝑡𝑖𝑣𝑒 𝑠ℎ𝑢𝑛𝑡

𝐵 ℎ = 𝐵 ÷ ℎ 𝑖𝑛𝑑𝑢𝑐𝑡𝑖𝑣𝑒 𝑠ℎ𝑢𝑛𝑡

Generator

𝑍𝐺 ℎ = 𝑅𝐺 + 𝑗ℎ𝑋𝐺

𝑅 + 𝑗𝑋 =𝑉2

𝑃 − 𝑗𝑄

𝑍𝑙𝑜𝑎𝑑ℎ = 𝑅 + 𝑗ℎ𝑋

𝑅1 = 𝑉2/𝑃

𝑅𝑙𝑜𝑎𝑑𝑠ℎ = 𝑅1

𝑋𝑙𝑜𝑎𝑑𝑠ℎ = 0.073ℎ𝑅1

𝑋𝑙𝑜𝑎𝑑𝑝ℎ =ℎ𝑅1

6.7𝑄𝑃

− 0.74

Nov. 06, 2013

IEEE 14 Bus System Diagram

Frequency Scan GUI Switching Transient Simulation GUI

PSSE Network Frequency Response Tool

ETAP CYME Our Tool

Case File ETAP case CYME case PSSE case

Frequency Scan

Positive-Sequence Impedance √ √ √

Zero-Sequence Impedance × × √

Driving Point Impedance √ √ √

Transfer Impedance × × √

Harmonic Calculation

Spectrum / Waveform Output √ √ √

Comply IEEE 519 Standard × √ √

Capacitor Loading per IEEE 18 × √ √

A Python software package developed by PDS-Lab which

analyzes network frequency response on the selected PSS/E

case file. Since the PSS/E itself does not have harmonic analysis

functions, this software can be treated as an 'add-on' of PSS/E.

Typical applications of this software include:

Identify Resonance

Filter Design

Verify Standards/Limits Compliance

Harmonic Problem Troubleshooting

Equipment Sizing

Equipment Loading Assessment

Interact with PSSE directly

Support up to 50000 buses

User friendly interface

Reliable validated result

Highly customizable

Easy install/uninstall

Read PSSE Case File

Retrieve steady state bus voltage V(0) from PSS/E

Modify PSSE case for each frequency

Apply a fault at bus i, Bus voltages after the fault (Vi and Vj), and fault

current at bus i (Ii) are retrieved from PSS/E fault analysis result.

Driving point impedance: Transfer impedance:

𝑍𝑖𝑖 =

𝑉𝑖 − 𝑉𝑖(0)

𝐼𝑖 𝑍𝑖𝑗 =

𝑉𝑗 − 𝑉𝑗(0)

𝐼𝑖

Option 1 Option 2

Add 2 Mvar capacitor

bank at bus 13

Add 1.8 Mvar capacitor

bank at bus 13

Very high impedance at 19th

harmonic, not good

Lower impedance at 19th harmonic,

better than option 1

Software Demo

Frequency scan result at bus 13 Frequency scan result at bus 13

Resonance: Because of the existence of both inductive and

capacitive components in the system, at certain frequencies,

resonance conditions might occur at some buses. If the

resonance occurs at a bus where a harmonic current is injected

into the system, an overvoltage will be observed.

Frequency Scan: A frequency scan is a plot of the driving-point

/ transfer impedance at a system bus versus frequency. The bus

of interest is one where a harmonic source exists. The frequency

scan is a very effective tool to detect resonances which appear as

peaks (parallel resonance) and valleys (series resonance) in the

plot of impedance magnitude vs. frequency.

One of the most common ways to obtain the harmonic impedance

is by using EMTP software. This requires a significant manual

labour to collect a huge amount of information and to model a

usually large interconnected network. Hence it is desirable to

have a software that can run frequency scan directly on a PSSE

case file, which stores all the system information and is well

maintained by utility companies.