May 31, 2006 1
Resource AdequacyCapacity Standard
Resource Adequacy Forum
Technical Committee
May 31, 2006
Background Image: Bennett, Christian Science Monitor
![Page 2: May 31, 20061 Resource Adequacy Capacity Standard Resource Adequacy Forum Technical Committee May 31, 2006 Background Image: Bennett, Christian Science](https://reader036.vdocuments.us/reader036/viewer/2022072114/56649f1f5503460f94c377e4/html5/thumbnails/2.jpg)
May 31, 2006 2
Objectives
• The capacity metric should be transparent and easy to calculate.
• The metric should be linked to a more sophisticated analysis (e.g. LOLP).
• Meeting the capacity target should assure that the power supply will adequately protect against capacity problems.
![Page 3: May 31, 20061 Resource Adequacy Capacity Standard Resource Adequacy Forum Technical Committee May 31, 2006 Background Image: Bennett, Christian Science](https://reader036.vdocuments.us/reader036/viewer/2022072114/56649f1f5503460f94c377e4/html5/thumbnails/3.jpg)
May 31, 2006 3
Proposed Capacity Metric
• A load/resource assessment (like the energy metric)
• But over the peak load period for each month (4 to 10 hours)
• In the form of a percent of resources that are surplus over the load or, in other words, a “surplus sustained peaking capacity”
![Page 4: May 31, 20061 Resource Adequacy Capacity Standard Resource Adequacy Forum Technical Committee May 31, 2006 Background Image: Bennett, Christian Science](https://reader036.vdocuments.us/reader036/viewer/2022072114/56649f1f5503460f94c377e4/html5/thumbnails/4.jpg)
May 31, 2006 4
Proposed Capacity Standard
• Metric – Surplus sustained-peaking capacity (%)– over the highest load period (for each month)– period duration is ??? hours – normal weather– under critical hydro (’37 water)
• Target – ??? percent (i.e. reserve margin)
![Page 5: May 31, 20061 Resource Adequacy Capacity Standard Resource Adequacy Forum Technical Committee May 31, 2006 Background Image: Bennett, Christian Science](https://reader036.vdocuments.us/reader036/viewer/2022072114/56649f1f5503460f94c377e4/html5/thumbnails/5.jpg)
May 31, 2006 5
Proposed Capacity Target
5-7% forContingency Reserve
X% for Outage Uncertainty
Y% forAdverse Weather andLoad Forecast Uncertainty
For example: California is using a 15 to 17% reserve margin but for a single hour peak
Z% for the Sustained Peaking Capacity Reserve Margin
![Page 6: May 31, 20061 Resource Adequacy Capacity Standard Resource Adequacy Forum Technical Committee May 31, 2006 Background Image: Bennett, Christian Science](https://reader036.vdocuments.us/reader036/viewer/2022072114/56649f1f5503460f94c377e4/html5/thumbnails/6.jpg)
May 31, 2006 6
Proposed Capacity Target(For January)
• 5 to 7% for Contingency Reserve
• 5% for Resource Forced Outages
• 10% for Adverse Weather (What should we plan for?)
• Yields a 20 to 22% target
![Page 7: May 31, 20061 Resource Adequacy Capacity Standard Resource Adequacy Forum Technical Committee May 31, 2006 Background Image: Bennett, Christian Science](https://reader036.vdocuments.us/reader036/viewer/2022072114/56649f1f5503460f94c377e4/html5/thumbnails/7.jpg)
May 31, 2006 7
Regional Capacity Assessment(L/R Bal = –1,500 aMW, LOLP = 5%)
January 2006 1-Hour 2-Hour 4-Hour 10-Hour
Hydro (’37) 26,850 21,131 20,541 18,686
Non-hydro 9,760 9,760 9,760 9,760
Firm Imports -1,218 -1,218 -1,218 -1,218
Spot Imports 3,000 3,000 3,000 3,000
Total Resource 38,392 32,673 32,083 30,228
Load (Avg) 25,633 25,506 24,847 22,691
Balance 12,759 7,167 7,236 7,537
Reserve 50% 28% 29% 33%
This is a scenario that is just adequate for energy needs.
![Page 8: May 31, 20061 Resource Adequacy Capacity Standard Resource Adequacy Forum Technical Committee May 31, 2006 Background Image: Bennett, Christian Science](https://reader036.vdocuments.us/reader036/viewer/2022072114/56649f1f5503460f94c377e4/html5/thumbnails/8.jpg)
May 31, 2006 8
Observations
• Acquiring resources to meet the energy needs of the region (i.e. LOLP = 5%) yields a 10-hour capacity reserve of 33% for January.
• 33% may be more than is needed based on our example,
• Which means that, for January, the region is energy constrained not capacity limited.
![Page 9: May 31, 20061 Resource Adequacy Capacity Standard Resource Adequacy Forum Technical Committee May 31, 2006 Background Image: Bennett, Christian Science](https://reader036.vdocuments.us/reader036/viewer/2022072114/56649f1f5503460f94c377e4/html5/thumbnails/9.jpg)
May 31, 2006 9
Statistical Approach
• Define a “peaking” event– Certain duration
– Certain magnitude
• Determine an acceptable likelihood for peaking events (i.e. like 5% for energy)
• Run a simulation model to assess the capacity LOLP• Plan resources to limit the LOLP to the acceptable
limit then calculate the resulting reserve margin.
![Page 10: May 31, 20061 Resource Adequacy Capacity Standard Resource Adequacy Forum Technical Committee May 31, 2006 Background Image: Bennett, Christian Science](https://reader036.vdocuments.us/reader036/viewer/2022072114/56649f1f5503460f94c377e4/html5/thumbnails/10.jpg)
May 31, 2006 10
Curtailment Events
Reliability Events by Game
0
1000
2000
3000
4000
3 12 12 12 12 12 12 15 15 18 18 22 22 25 25 25 25 25 25 33 33 33 33 34 36 36 36 36 36 36 36 37 39 39 39 39 39 39 39 39 41 44 44 46 46 46
Game
Cur
tailm
ent (
MW
)
Seattle
![Page 11: May 31, 20061 Resource Adequacy Capacity Standard Resource Adequacy Forum Technical Committee May 31, 2006 Background Image: Bennett, Christian Science](https://reader036.vdocuments.us/reader036/viewer/2022072114/56649f1f5503460f94c377e4/html5/thumbnails/11.jpg)
May 31, 2006 11
LOLP Type StatisticsTypes of “peaking” events No. of
GamesLOLP
(%)
At least 1 hour of curtailment 18 36
At least one hour with curtailment > 1,000 mw 11 22
At least five separate hours with curtailment > 1,000 mw 5 10
At least ten separate hours with curtailment > 1,000 mw 2 4
At least one hour with curtailment > 2,000 mw 2 4
At least one hour with curtailment > 3,000 mw 1 2
At least two consecutive hours, each > 1,000 mw 8 16
At least three consecutive hours, each > 1,000 mw 5 10
At least four consecutive hours, each > 1,000 mw 2 4
Energy: at least 28,000 mw-hrs of curtailment 2 4
![Page 12: May 31, 20061 Resource Adequacy Capacity Standard Resource Adequacy Forum Technical Committee May 31, 2006 Background Image: Bennett, Christian Science](https://reader036.vdocuments.us/reader036/viewer/2022072114/56649f1f5503460f94c377e4/html5/thumbnails/12.jpg)
May 31, 2006 12
Capacity LOLP
• One hour > 1,000 mw => LOLP = 22%
• One hour > 2,000 mw => LOLP = 4%
• One hour > 3,000 mw => LOLP = 2%
• One hour > 4,000 mw => LOLP = 0%
• 4 hours, each > 1,000 mw => LOLP = 4%