topic1-2 refrigeration cycle
TRANSCRIPT
Topic1-2 Refrigeration Cycle1. Carnot Refrigeration cycle2. Coefficient of performance (COP)3. Conditions for highest COP4. Temperature limitations5. Carnot heat pump6. Using vapor as a refrigerant7. Wet versus dry compression
8. Expansion process 9. Properties of refrigerants 10. Standard vapor-compression cycle
11. Performance of the SVC cycle12. System Efficiency Index (SEI)
13. Condenser and evaporator temperature differences14. Liquid Subcool Heat exchanger 15. Subcooling and superheating
1
16. Analysis of Carnot refrigeration cycle17. Comparison between Carnot & standard VCRS 18. Actual vapor-compression cycle19. Multi-stage cycles20. Non vapor-compression cycles20.1 Trans-critical carbon dioxide cycle
20.2 Expendable refrigerant cooling system20.3 Absorption cycle20.4 Air cycle
20.5 Stirling cycle20.6 Thermoelectric cooling20.7 Magnetic refrigeration20.8 Steam jet refrigeration20.9 Vortex tube21. Natural Refrigeration
1. Carnot Refrigeration cycle
2
Carnot cycle: thermodynamically reversible processes
Net work
2
1-2 Adiabatic compression
Heat from low-Temp. source
Heat to high-Temp. sink
Tem
per
atu
re, K
Entropy, kJ/kgK
1
23
4
1
23
4WorkCompressor
2-3 Isothermal rejection of heat
3-4 Adiabatic expansion4-1 Isothermal addition of heat
Work
Turbine
1-2 Adiabatic reversible compression = isentropic compression
3-4 Adiabatic reversible expansion = isentropic expansion
-Standard of comparison- Guide of T to max eff.
Refrigeration
2. Coefficient of performance (COP)
3
Efficiency = Output / Input → Heat Engine = Wout/Qin
Net work
3
Tem
per
atu
re, K
Entropy, kJ/kgK
1
23
4
reversible process: qrev = ∫Tds :
Refrigeration cycle: input = net workOutput = q2-3 – wasteDesired output = q4-1 – useful refrigeration
HE = (TH - TL)/ TH
TH
TL
Coefficient of performanceCOP = desired output/input
COPRefrigeration Carnot
= T1(s1 – s4)/[(T2 – T1)(s1 – s4)]= T1 / (T2 – T1)= TL / (TH - TL)
s1 = s2s3 = s4
3. Conditions for highest COP
low T2 → high COP
4
COPR Carnot = T1 / (T2 – T1)
Refrigeration
4
Net work
4
Tem
pe
ratu
re, K
Entropy, kJ/kgK
1
23
4
T2
T1
s1 = s2s3 = s4high T1 → high COP
T1 → more effect upon COP than T2
4. Temperature limitations
Ex: a cold room at -20C & reject heat to the atm. at 30C
5
Tem
per
atu
re, K
Entropy, kJ/kgK
1
23
4
T2
T1
253 K cold room
303 K atmosphere
2-3 heat rejection processT2 > 303 K
4-1 refrigeration processT1 < 253 K
high COP → low T2 but T2 > 303 K
high COP → high T1 but T1 < 253 K
→ T2 – 303 = T1
→ 253 – T1 = T2
T1
T2
What can we do on keeping t as small as possible?
Heat exchanger: Condenser → qc = (UA)c T1
Heat exchanger: Evaporator → qe = (UA)e T2 = (UA)e Tlm
= (UA)c Tlm
5. Carnot heat pump
Heat pump: same equipment as a refrigeration system- delivering heat at high Temp.
6
Coefficient of performanceCOP = desired output/input
Net workTe
mp
era
ture
, K
Entropy, kJ/kgK
1
23
4Heat rejected
COPHeat Pump Carnot = T2 / (T2 – T1) = COPR + 1Performance factor = COPR + 1
Performance factor- vary from 1 to
6. Using vapor as a refrigerant
Refrigerant: gas, i.e. air
7
Tem
per
atu
re, K
Entropy, kJ/kgK
1
2
3
4
x
Cold room
Atmosphere
y
2-3 constant-pressure heating4-1 constant-pressure cooling
Different from Carnot cycle by area x and y
area x and y → decrease COP
6. Using vapor as a refrigerant
8
To keep rectangle shape as Carnot cycle:
Refrigerant condenses during heat-rejection at const. T, Pand boil during refrigeration at const. T,P
Isothermal heat-rejection and refrigeration
→ Condenser
→ EvaporatorRefrigerant operates between liquid and vapor states.
Tem
per
atu
re, K
Entropy, kJ/kgK
Cold room
Atmosphere
1
23
4
Saturated liquid
Saturated vapor
7. Wet compression versus dry compression
Wet compressionLiquid refrigerant may damage valves or cylinder head.Droplets of liquid may wash the lubricating oil from cylinder wall
9
Tem
per
atu
re, K
Entropy, kJ/kgK
Superheat horn
1
2
3
4
Dry compressionSuperheat horn – more work required for dry compression
8. Expansion process Constant-enthalpy throttling -- Isenthalpic process
10
Tem
per
atu
re, K
Entropy, kJ/kgK
1
2
3
4
Expansion engine: 1. Small work compared to compression work2. Difficulties of lubrication intrude when a fluid of two-phase drives the engine3. Not economic for work done compared to cost of expansion engine
Throttling device: reducing pressure by valve or other restriction
9. Properties of refrigerants : low boiling point
11
Pre
ssu
re,
kPa
Enthalpy, kJ/kg
Critical point
t = constant
Saturated liquid
Saturated vapor
Mollier (Pressure-enthalpy) diagram of a Refrigerant
12
1
23
4
Isobaric
Isobaric
Net work
Refrigeration effectTe
mp
erat
ure
, K
Entropy, kJ/kgK
1
23
4
T2
T1
Carnot refrigeration cycle
high T1, low T2 → high COP
COPR Carnot = T1 / (T2 – T1)
T1 → more effect on COP than T2
12
10. Standard vapor-compression cycle
13
Tem
per
atu
re, K
Entropy, kJ/kgK
1
2
3
4
Process 1-2: Isentropic compression of saturated vapour in compressor Process 2-3: Isobaric heat rejection in condenser Process 3-4: Isenthalpic expansion of saturated liquid in expansion device Process 4-1: Isobaric heat extraction in the evaporator
Pre
ssu
re,
kPa
Enthalpy, kJ/kg
1
23
4
Condensation
Exp
ansi
on
Evaporation
Isen
thal
pic
Isobaric
Isobaric
Carnot refrigeration cycle
The standard vapor-compression cycle
14
Mollier (Pressure-enthalpy) diagram
Pre
ssu
re,
kPa
Enthalpy, kJ/kg
1
23
4
Condensation
Exp
ansi
on
Evaporation
1
2
3
4
PowerQc
Qe
Power= ሶ𝑚(h2-h1)Qe = ሶ𝑚(h1-h4)
Qc = ሶ𝑚(h2-h3)
11. Performance of the standard vapor-compression cycle
15
Pre
ssu
re,
kPa
1
23
4
Condensation
Exp
ansi
on
Evaporation
Enthalpy, kJ/kg
Work of compression = wc = h2 – h1
Pc = ሶ𝑚(h2-h1)
Heat rejection rate = qc = h2 – h3
Qc = ሶ𝑚(h2-h3)
Refrigeration effect = qe = h1 – h4
Qe = ሶ𝑚(h1-h4)
COP = qe/wc
Volume flow rateper kW of refrigeration = ሶ𝑚vsuc /Qe
Power per kW of refrigeration = P/Qe = 1/COP
Example 1 A standard vapor-compression cycle developing 50 kW of refrigeration using refrigerant 22 operates with a condensing temperature of 35C and an evaporating temperature of -10C. Calculate (a) the refrigerating effect in kilojoules per kilogram, (b) the circulation rate of refrigerant in kilograms per second, (c) the power required by the compressor in kilowatts, (d) the coefficient of performance, (e) the volume flow rate measured at the compressor suction, (f) the power per kilowatts of refrigerant, and (g) the compressor discharge temperature.
Data: VCC, Qe, R22, tcond, tevap
Assume: standard VCC; isentropic compression, isobaric, isenthalpic processes
Method: evaporator, energy balance, (a) qe = h1-h4
evaporator, mass balance, (b) ሶ𝑚 = Qe/qe
compressor, energy balance, (c) Pc = ሶ𝑚(h1-h2)(d) COP = Qe/Pc
(e) Vsuc = ሶ𝑚vg@pe, pe= psat@Te
(f) P/Qe = 1/COP(g) Tdischarge = T2 = T@(pc, s2=s1), pc= psat@Tc
Pre
ssu
re,
kPa
1
23
4
Enthalpy, kJ/kg
35C= Tc
-10C= Te
(a)qe (b) ሶ𝑚 (c) Pcomp (d) COP (e)vsuc (f)P/Qe (g)Tdischarge
16
17
-10 C = tevap
35 C= tcond
1
2
h1=402 h2=435h4=243
T2=57C
3
4
17
Calculation: (a) qe = h1-h4 = 59 kJ/kg(b) ሶ𝑚 = Qe/qe = 0.315 kg/s(c) Pc = ሶ𝑚(h1-h2) = 10.3 kW(d) COP = Qe/Pc = 4.86(e) Vsuc = ሶ𝑚vg@pe = 20.4 L/s(f) P/Qe = 1/COP = 0.207(g) Tdischarge = T2 = 57C
h@0 C =200 kJ/kg
Example 1 VCC R22 at 35C and -10C
pe=355 kPa
pc=1355 kPa
Example 2 A standard vapor-compression refrigeration cycle using R22 operates with a condensing temperature of 35C and an evaporating temperature of -10C. If efficiency of compression is 70%, calculate (h) the actual COP, (i) actual discharge temperature T2’ and (j) System Efficiency Index, SEI = COPact/COPCarnot.
SEI is the ratio between the actual COP and the Carnot COP with reference to the cooling load and outside air temperatures, i.e. when the heat exchanger temperature differences, ΔT = 0, Tload = Te , To = Tc .
Assume: actual compression, isobaric, isenthalpic processes
Method: COPact = (h1-h4)/Pc,act = (h1-h4)/(h1-h2’)compression efficiency, c = (h2-h1)/(h2’-h1) = Pc/Pc,a
(h2’-h1) = (h2-h1)/c = (435-403)/0.7 = 47 kJ/kg
(h) COPact = (402-243)/47 = 3.40
T2’ = T@(pc, h2’), h2’ = 402 + 47 = 449 kJ/kg
T2’ = 74C
SEI = COPact/COPCarnot
COPCarnot = Te/(Tc-Te) = (-10+273)/(35-(-10)) = 5.84
(j) SEI = 3.40/5.84 = 0.582
Pre
ssu
re,
kPa
1
23
4
Enthalpy, kJ/kg
35C= Tc
-10C= Te
18
2’
12. System Efficiency Index (SEI) = COPactual/COPCarnot@ΔT=0
19
13. Condenser and evaporator temperature differencesCOP values for R22 cooling at -10C = Tload
with an outside air temperature of 35C = To
Varying Te and Tc forT1 = Tload - Te = T2 = To - Tc = T
Pre
ssu
re,
kPa
1
23
4
Enthalpy, kJ/kg
45C= Tc
-20C= Te
1
23
4
Enthalpy, kJ/kg
40C= Tc
-15C= Te
Tload
T = 5 C
To
Tload
T = 10 C
To
2’
2’
Pre
ssu
re,
kPaT at evaporator and condensor, °C 0
Evaporating temperature, °C -10
Condensing temperature, °C 35
Temperature lift = T c - Te, °C 45
Evaporating pressure, pe, kpa 355
Condensing pressure, Pc, kPa 1355
Pressure ratio = pc/pe 3.82
Carnot COP (refrigeration cycle) 5.84
h1 = hg,@Te, kJ/kg 402
s1 = sg,@Te, kJ/kgK 1.767
h2, kJ/kg 435
Discharge temperature, T2, °C 57
h3 = hf,@Tc kJ/kg 243
Refrigerating effect, kJ/kg 159
work for compressor, kJ/kg 33
COP, standard vapor compression cycle 4.86
compression efficiency, % 70
actual work for compressor, kJ/kg 47
COP, with 70% compression efficiency 3.40
System efficiency index, SEI 0.582
actual h2', kJ/kg 449
Actual discharge temperature, T2', °C 74
10
-20
45
65
244
1729
7.08
3.89
398
1.784
447
77
257
142
48
2.92
70
69
2.04
0.350
467
95
5
-15
40
55
296
1534
5.19
4.69
400
1.775
441
67
250
150
41
3.70
70
58
2.59
0.443
458
82
20
80 kPa = pe
1000 kPa = pc
1
3
h1=1413 h3=1783h@0 C =200 kJ/kg
h6=317
Example 3 Calculate the power needed to compress 1.2 kg/s of ammonia to saturated vapor at 80 kPa to 1000 kPa
Assume: standard VCCCalculation: Pc = ሶ𝑚(h1-h2) = -444 kWQe = ሶ𝑚(h1-h4) = 1315 kWCOP = Qe/Pc = 2.96COPCarnot = Te/(Tc-Te) = 6.18SEI = COP/COPcarnot = 0.77Tdischarge = T2 = 143C
14. Liquid Subcool Heat exchanger (LSHX)
21
Subcool liquid from condenser with suction gas from evaporator
Heat balance: h3-h4 = h1-h6
Refrigerating effect: h6-h5 = h1-h3
qe = h6-h5
21
22
15. Subcooling and superheating
1
23
4 1’
2’3’
4’
Superheating by heat -transfer from cold room →qe
-exchange with pipeline → loss-transfer from subcool liquid → 0→wc in some refrigerant, i.e.→Tdischarge affects lubrication→ Dry vapor to prevents entry of liquid droplets into compressor
cold room Subcooling by heat transfer to
surrounding or to suction vapor→qe by reduce throttling loss→ Reduce flash gas → lower
pressure drop in evaporator- ensures that only liquid enters into throttling device leading to its efficient operation.
atmosphere
Example 4 ระบบท ำควำมเยน็แบบอดัไอใช้ R22 มอุีณหภมูทิี่ Evaporator Te = 0C และที่Condenser Tc = 40C ใหห้ำ a) sketch เสน้ refrigeration cycle บน p-h diagram, b) COP ของ Carnot cycle, c) Refrigeration effect, 2d) Work of compression, e) อุณหภมูขิอง discharge, f) COP ของ standard vapor-compression refrigeration cycle, g) ถำ้น ำ Liquid-to-suction heat exchanger มำใชเ้พือ่ superheating เพิม่ 10C แลว้ subcool คำ่อุณหภมูทิีข่ำออก Condenserเป็นเทำ่ใด, h) Refrigeration effect เมือ่ใช ้LSHX และ i) Work of compression เมือ่ใช ้LSHX
Data: VCC, R22, Te, Tc ,
Assume: standard VCC; isentropic compression, isobaric, isenthalpic processes
Method: (b) COPcarnot = T1 / (T2 – T1) = 6.83 (T, K)
Evaporator (c) qe = h1-h4 = 406-250 = 156 kJ/kg
compressor (d) wc = h1-h2 = 406-433 = -27 kJ/kg
(e) Td = 58C
(f) COP = qe/wc = 5.82
LSHX, h3-h3’ = h1’-h1 = h = 8 kJ/kg
(g)Tsp = T1’-T1 = 10C, Tsc 6C
T3’ = 40-6 = 34C
(h) qe,LSHX = qe +h = 156+8 = 164 kJ/kg
(i) Te = 0+10C, wc = h2’-h1’ = 443-414 = 29 kJ/kg
Pre
ssu
re,
kPa
1
23
4
Enthalpy, kJ/kg
3’
1’
(a)p-h (b) COPcarnot (c) qe (d) wc (e)Td (f)COP (g) t3’ (h) ሶ𝑚
40C= Tc
0C= Te
23
3
3’ 1
1’
2’
24
0 C = Te
40 C= Tc
1
2
h1=406 h2=433h4=250
T2=58C
3
4
s1=s2=1.752
1’
3’2’
h2’=443
h3’=242
LSHX, h3-h3’ = h1’-h1 = h = 8 kJ/kg
qe,LSHX = qe +h = 156+8 = 164 kJ/kg
h1’=414
wc = h2’-h1’ = 443-414 = 29 kJ/kg
high T1, low T2 → high COP
25
COPR Carnot = T1 / (T2 – T1)
Refrigeration
25
Net work
25
Tem
pe
ratu
re, K
Entropy, kJ/kgK
1
23
4
T2
T1
s1 = s2s3 = s4
T1 → more effect on COP than T2
16. Analysis of Carnot refrigeration cycle
T1
T2
2626
17. Comparison between Carnot & standard VCRS
COPStandard VCRS =COP = qe / wcomp = (h1 – h4)/(h2 – h1)
R = SEI = COPStandard VCRS / COPR Carnot
COP = (hg@Te – hf@Tc)/(hs1=s2 – hg@Te)
COP asTevap or Tsuction
COP as Tcond
SEI =System Efficiency Index
27
1
23
4
Isen
thal
pic
Isobaric
Isobaric
Standard VCRS cycle
As Tevap
1. RE(qe)2. wcomp then COP 3. Tdischarge
4. qcond
5. %flash gas bcoz %x
6. ሶ𝑚 bcoz v (L/kg)
1’
2’
4’
27
Refrigeration effect
Net work
Refrigeration effect
28
Tem
per
atu
re, K
Entropy, kJ/kgK
1
23
4
Carnot refrigeration cycle
Pre
ssu
re,
kPa
Enthalpy, kJ/kg
Standard VCRS cycle
1
2
3
4
T2
T1
Irreversibility due to 1) non-isothermal heat rejection (process 2-3) 2) isenthalpic throttling (process 3-4)
Throttling loss
Superheat horn
Superheat horn – more work required for dry compression, high Td
Throttling loss - flash gas, reduction in refrigeration effect and increase more work because irreversibility
qewc
17. Comparison between Carnot & standard VCRS
Good for heat pumps
wc
18. Actual vapor-compression cycle
29
Discharge line: gas, p is a penalty on compressor power
Liquid line: liquid, smaller diameter, more p → liquid flashes in to vapor →expansion device will not work properly
Suction line: gas, p is a penalty on efficiency, reduce ps to comp.
18. Actual vapor-compression cycle
30
Irreversibility due to 1. Pressure drops in evaporator, condenser and LSHX 2. Pressure drop across suction and discharge valves of the compressor 3. Pressure drop and heat transfer in connecting pipe lines 4. Heat transfer in compressor
4-1d → pressure drop in evaporator1d-1c → Superheat of vapor in evaporator 1c-1b → Useless superheat in suction line
1b-1a → Suction line pressure drop 1a-1 → Pressure drop across suction valve
1-2 → Non-isentropic compression 2-2a → Pressure drop across discharge valve
2a-2b → Pressure drop in the delivery line
2b-2c → Desuperheating of vapor in delivery pipe
2b-3 → Pressure drop in the condenser
3-3a → Subcooling of liquid refrigerant
3a-3b → Heat gain in liquid line
Actual systems differ from standard cycles -- foreign matter such as lubricating oil, water, air, particulate matter→ pressure drop, heat transfer coefficient in evaporator
31
1
2
3
4
4-1d → pressure drop in evaporator
1d-1c → Superheat of vapor in evaporator
1c-1b → Useless superheat in suction line
1b-1a → Suction line pressure drop
1a-1 → Pressure drop across suction valve
1-2 → Non-isentropic compression
2-2a → Pressure drop across discharge valve
2a-2b → Pressure drop in the delivery line
2b-2c → Desuperheating of vapor in delivery pipe
2b-3 → Pressure drop in the condenser
3-3a → Subcooling of liquid refrigerant
3a-3b → Heat gain in liquid line
32
Discharge line: vapor line
Liquid line: liquid
Suction line: vapor line
Standard cycle
18. Actual vapor-compression cycle
2-2a → Pressure drop across discharge valve
2a-2b → Pressure drop in the delivery line
→wc (compressor work)→ Tdischarge – compressor life
1a-1 → Pressure drop across suction valve
1-2 → Non-isentropic compression
suction pressure (ps) →specific volume → compressor volumetric efficiency (v)→wc
→wc
→ liquid flashes into vapor qewc
→ expansion device will not work properly
4-1d → pressure drop in evaporator
1d-1c → Superheat of vapor in evaporator
1c-1b → Useless superheat in suction line 1b-1a → Suction line pressure drop
3-3a → Subcooling of liquid refrigerant
3a-3b → Heat gain in liquid line
→ efficient operation→ qe
2b-2c → Desuperheating of vapor in delivery pipe
2b-3 → Pressure drop in the condenser
→wc but smaller than that in vapor line
need cooling
Pipe design for small pdrop
Reduce pdrop by velocity flow or pipe size→ heat transfer coefficient in evaporator*minimum velocity is required to carry lubricating oil back to compressor
19. Multi-stage cycles
33
1. High pr; ratio of suction to discharge pressure is high enough to cause a serious
2. Low v or high Td; drop in volumetric efficiency or an unacceptably high discharge temp.
Two-stage cycle
a) with intercooling
b) with flash-gas removal and intercooling
c) with flash-gas removal
a) with intercooling and liquid-subcooler
20. Non vapor-compression cycles
34
20.1 Trans-critical carbon dioxide cycleTcr = 31C; heat rejection near Tcr – low refrigerating effectGas cooler as condenser without condensation
Mollier diagram for R744 showing transcritical cycle with evaporation at –10°C, compression to 100 bar and gas cooling to 40°C
120C40C
-10C
Liquid formation only takes place duringexpansion to the lower pressure level.
Actual compression process with compression efficiency 70-80%Isentropic processAt lower Td = 100°C
35
Total loss refrigerant: liquid nitrogen, carbon dioxide
20.2 Expendable refrigerant cooling system
Transportation refrigerationof perishable goods. Base system uses liquid, non-toxic, low temperature refrigerant. Low-cost liquid can be used as a refrigerant is then dumped into the atmosphere. This is called chemical or open cycle cooling.
Carbon dioxide is below triple point: snow or gasLiquid nitrogen released at -199Ccarbon dioxide released at -78C
36
20.3 Absorption cycle
removing evaporated refrigerant vapor without compressor
Lithium bromide - water
1810 J. Leslie - H2SO4 -absorbent, water-refrigerant
1860 F. Carre - aqua-ammonia absorption system. Water is a strong absorbent of NH3
Solar energy based absorption refrigeration systems in 1950s
GeneratorAbsorberPump
37
20.4 Air cycle
Air cycle refrigeration works on the reverse Brayton or Joule cycle. Air is compressed and then heat removed; this air is then expanded to a lower temperature.Expansion turbine can be useful energy to run compressors.Main application; air conditioning and pressurization of aircraft.Low COP
38
20.5 Stirling cycle
The Stirling cycle is an ingenious gas cycle which uses heat transferred from the gas falling in temperature to provide that for the gas rising in temperature.A detailed explanation of the cycle is referred to Gosney (1982) and Hands (1993). The Stirling cycle has been successfully applied in specialist applications requiring low temperatures at very low duties.
Portable refrigeration; The Free Piston Stirling Cooler (FPSC
invented in 1964) is a completely sealed heat transfer system that has only two moving parts (a piston and a displacer), and which can use helium as the working fluid.
39
20.6 Thermoelectric cooling
1821-- T.J. Seebeck - an electro motive force (emf)1834 -- J. Peltier - the reverse effect observedThe passage of an electric current through junctions of dissimilar metals causes a fall in temperature at one junction and a rise at the other.
1838-H.F.E. Lenz froze a drop of water using antimony and bismuth 1857– W. Thomson -- Thomson effect1949-A. F. Ioffe : thermoelectric refrigeration systems using semiconductors
1960s- mainly used for storing medicines, vaccines, in electronic cooling Some large refrigeration capacity systems such as a 3000 kcal/h air conditioner and a 6 ton capacity cold storage were also developed.
40
20.7 Magnetic refrigeration
Magnetic refrigeration depends on the magnetocaloric effect, which is the temperature change observed when certain magnetic mater-ials are exposed to a change in magnetic field. Magnetic refrigeration is a research topic, and historically has been used at ultra-low temperatures. Only recently has it been seen as a possible means of cooling at near room temperatures. An overview of magnetic refrigeration is given by Wilson et al. (2007)Ref. Wilson N , Ozcan S , and Sandeman K , Overview of magnetic refrigeration, IOR , 2006–7.
41
20.8 Steam jet refrigeration
water is sprayed into a low pressure chamber - evaporate - required good vacuum- low- grade energy process steam in chemical plants or a boiler 1838 F. Pelletan – patent of steam compression by a jet of motive steam. 1907 – ejectors - high velocity steam jet (≈ 1200 m/s)
42
20.9 Vortex tube
1931 G. Ranque – “vortex effect” tangential injection of air into a cylindrical tube Temperatures as low as −46°C and as high as 127°C are possible.
21. Natural Refrigeration
43
1.1 Use of Ice :Natural convection of air
1.3 Evaporative cooling :evaporation of water
1.4 Salt solution:Water + saltNaCl → -20C CaCl2 → -50 C
1.2 Dry ice : CO2 -78C