DIY – 15 Amp Portable Generator Transfer Switch
-------------------------------------------------------------------------------------------------
WARNING
You MUST read these warnings before proceeding.
This is not a task for the electrically uneducated or inexperienced. Electricity can
and does KILL. It is important to keep in mind that electricity can kill, maim and
damage through electrical shock and through such things as fire via arc-induced
burning and high resistance connections. It is also very important to note that if
you incorrectly install transfer equipment, or fail to install transfer equipment,
you can easily harm or kill utility workers and neighbors outside of your
residence through “back feeding.” If you are not comfortable or technically
qualified for this task, spend the few extra dollars to purchase purpose built
equipment and pay a professional to install it.
While proper installation of any electrical components is a major life safety issue,
improper or poor installation can also cause extensive and quite expensive
damage to equipment.
You must be familiar with national codes, i.e. NFPA 70 – National Electric Code
and ICC International Residential/Building Codes, and with any local and/or
utility restrictions, codes or amended adoptions. Yes, that’s right, some utility
companies require notification, inspection and adherence to special utility
requirements for installation of a standby generator (a portable wired into any of
the residence’s circuits is considered a standby generator.)
The information provided here is for INFORMATIONAL PURPOSES ONLY and
should not be considered or inferred as instructional in nature. Basic electrical
knowledge and installation steps were omitted.
-------------------------------------------------------------------------------------------------
TRANSFER SWITCH BASICS
What is a transfer switch as used with a standby generator and your home? Well, the
simple answer is that it isolates the generator from the home’s electric utility service
and vice versa. Without a transfer switch, the only way to tie a generator into your
home’s electrical system is to perform the very dangerous and likely illegal act of “back
feeding.” Back feeding is done by connecting the output of your generator to your
home’s electrical system, typically by plugging into a receptacle. This is dangerous for
several reasons. The first reason that this is unacceptable is that, with a large enough
generator, can likely overload the circuit that you are back feeding through resulting in
damage, fire or injury. Another reason that one must be mindful of the dangers of
back feeding is the simple fact that you can energize not only your entire house, but
your neighborhood and even primary service lines. It is important to note that when
you back feed, the same transformer that reduces line voltages to your household
voltages can work in reverse. That is, your 120 volts put out by your generator can be
stepped up to line voltage back feeding through a transformer. You could imagine how
dangerous this can be for utility workers repairing downed lines, damaged equipment,
etc.
The basic function of a transfer switch in a standby generator system is to isolate two
separate feed sources for a load(s) from each other, preventing any chance of one
power system feeding the other and vice versa. The following graphic illustrates a
basic schematic of a single transfer switch. The illustrated switch is a single pole,
double throw (SPDT) type. A common example of a SPDT switch is a three-way switch
found in the home. As drawn, the load/appliance is connected to the electric service of
the building and/or residence. The generator supply in this example is isolated from
the load and the electric service. When the transfer switch is actuated/switched, the
connection between the electric service/line power will “break” and then the switch will
“make” the connection between the load and the generator. Note the terms “make”
and “break” for these are important. It is possible to have two different types of SPDT
switches: make before break and break before make. A make before break switch will
actually have a brief period of time during switching where both the line power and the
generator will be connected. The break before make switch, the common type,
theoretically should never allow the connection of the two power sources. Obviously,
this is the type of switch that we need. The three-way switch mentioned earlier is
typically this type of SPDT switch.
There are several companies that manufacture and sell preassembled transfer switches,
basically, off-the-shelf solutions. Two of these companies are GenTran and Reliance.
For what these switches are, sets of SPDT switches and some push button breakers (for
the basic manual options), I have yet to meet anyone that thought these were a
bargain. Based on my needs and what is available on the market, I opted to design
and install a much more economical, custom matched to my needs and just as safe for
property and life transfer switch system.
TRANSFER SWITCH DESIGN & INSTALLATION
The above illustration captures my transfer switch design. Some important safety
oriented characteristics to note regarding this design:
Note that all boxes, grounded receptacles and grounded switches are bonded to
the generator’s ground and in turn bonded to the ground bus at the electric
service panel for my house.
The neutral from the generator is bonded to the neutral bus of the service panel
which, in turn, is bonded to the ground bus of the service panel. Note: My
generator, Honda Eu2000i, does not have a neutral bonded to ground at its feed
points. In this particular example, you do NOT want to bond the neutral and
ground at the generator, Honda Eu2000i, if you are bonding the neutral and
ground buses at the service panel. Some generators come from the factory with
a neutral to ground bond, but that is not so in my case. In my example, if I
were to bond the neutral and ground at my generator and have the neutral
grounded at the panel, I now have two different paths for return current to flow
to my generator. Return current on the ground will create voltage on the ground
and that is NOT good. For now, you theoretically have an “energized” ground
and this is both a life safety and property concern.
All circuits being dual served are 15 amp in size in the main service panel. While
the generator has 20 amp circuit protection, this is too much for my home’s 15
amp branch circuit wiring. So, I would be able to overload a 15 amp branch
circuit with 19.9 amps and never trip the generator circuit protection out. Also,
keep in mind that 15.1 amps will not instantaneously trip a 15 amp breaker. As
a matter of fact, 15 amps on a 15 amp protected circuit could take minutes or
longer before tripping. It is also important to note that a 20 amp breaker will
not trip as fast with higher currents as what a 15 amp breaker would. All of
these concerns/issues could be major fire safety hazards. To prevent any issues,
each transfer switch’s generator side line is protected by a 15 amp breaker (All of
the 15 amp circuits utilize 14/2 W/ Ground wiring).
The feed cable (12/2 W/ Ground) from the L5-20R receptacle (where the
generator is hooked up outside) and the receptacle itself are sized to
accommodate the 20 amp protected circuit provided by the generator as is the
utility receptacle.
The transfer switches are 20 Amp models with Heavy Duty Contacts to prevent
welded or sticking contacts in order to meet the break before make requirement
as mentioned above.
The basic “flow” of the system is as follows:
Generator > Service Cable > Twist-Lock Receptacle > Split to Utility Outlet & Generator
2 Breaker, 4 Circuit Load Center > Transfer Switch > Load (E.g. Appliance)
The materials list is as follows:
Outdoor Receptacle (See Part 2 below.)
L5-20I Flanged Insert Receptacle
Outdoor, Deep Receptacle Box
Hubbell Flanged Insert Outdoor Receptacle Box Cover
Vinyl Siding J-Block
Generator Load Center
Cutler-Hammer 2 Breaker, 4 Circuit Load Center (Cutler-Hammer to match
existing service panel)
Cutler-Hammer Twin 15/15 Amp BR Breakers
Utility Outlet
Single Metal Box
20 Amp 120V Duplex Receptacle
Duplex Receptacle Cover
Transfer Switches
20 Amp Heavy Duty Three-Way SPDT Switches
Double Metal Boxes
Double Switch Covers
Miscellaneous: Wiring, Conduit, Etc.
12/2 W/ Ground
14/2 W/ Ground
3/4” EMT Conduit
3/4” Conduit Clamps
3/4” Conduit Setscrew Connectors
Wire Nuts & Electrical Tape
At a minimum, your design, layout and installation must comply with the current
revision of the National Electric Code. In my case, the current revision that must be
complied with is NFPA 70 – National Electric Code 2008. Remember, your local
jurisdiction may require drawings, permitting, inspections and requirements in excess of
code requirements.
Some of the items of importance from the National Electric Code that apply to this
installation are as follows:
Grounding Requirements - Article 250.20 (Previously discussed.)
Article 100 Definitions
Separately Derived System. A premises wiring system whose power is derived from a
source of electric energy or equipment other than a service. Such systems have no
direct electrical connection, including a solidly connected grounded circuit conductor, to
supply conductors originating in another system. (My system is a non-separately
derived system. This definition later determines various requirements for installation.)
Article 312.8 Enclosures for Switches or Overcurrent Devices
Enclosures for switches or overcurrent devices shall not be used as junction boxes,
auxiliary gutters, or raceways for conductors feeding through or tapping off to other
switches or overcurrent devices, unless adequate space for this purpose is provided.
The conductors shall not fill the wiring space at any cross section to more than 40
percent of the cross-sectional area of the space, and the conductors, splices, and taps
shall not fill the wiring space at any cross section to more than 75 percent of the cross-
sectional area of that space. (This Article covers the use of wire nuts inside of a service
panel. It is OK given compliance with this Article is maintained.)
Article 702 Optional Standby Systems
Scope: The provisions of this article apply to the installation and operation of optional
standby systems.
The systems covered by this article consist of those that are permanently installed in
their entirety, including prime movers, and those that are arranged for a connection to
a premises wiring system from a portable alternate power supply. (This Article and its
various sections dictate the actual design, installation and integration of a standby
power system, i.e. generator, into your existing electrical distribution system.)
Following the design schematic above, installation and integration was actually very
rudimentary and easy. One important safety note here is that you should NEVER work
inside of a “hot”/energized panel. It is best if you can not only de-energize a service
panel that you are working in but lock out the main disconnect as well! All it takes is a
mistake or inattention lasting only a few milliseconds to permanently change your life!
My main service panel for the house…
Installation of the transfer switches. Note that I have number markers on the wires to
assist in keeping the installation straight as well as troubleshooting if ever required…
It is important to keep your routing clean and out of the way…
The finished product. Note I have a copy of the basic schematic in an envelope at the
transfer switch…
Outside hookup to the standby generator transfer system…
The parts that you see here are as follows:
Hubbell 2315 Flanged Insert – This is the receptacle that is basically a recessed
male plug.
Hubbell 2313 Equivalent L5-20C Connector – This is the receptacle end of the
patch cord.
Hubbell WP-2 Flanged Cover Plate – This is the spring-loaded flip cover for the
flanged insert.
Note: The above listed parts, if purchased through a catalog supply house can easily
total more than $140. However, in this instance, Ebay is your friend! I picked up all
three pieces above for approximately $40 shipped.
The Honda Eu2000i and patch cord that will power it all…
IMPORTANT NOTE:
It is very important that you utilize the proper flanged inlet and female connector for
the hookup on the exterior of dwelling and the patch cord respectively. The inlet and
connector are not readily found at Lowe’s, Home Depot or similar “Big Box” store. It is
easy to want to cut corners and use a standard receptacle and plug. However, this is
very, very dangerous. If you use a standard receptacle and plug, you will end up with
what is labeled as a “suicide plug” or “suicide cord”. That is, you will wind up with a
patch cord that has two male plugs rather than one female connector and one male
plug. In turn, there is potential for one set of the exposed prongs of the plugs to be
energized while operating the generator if installed as detailed in this post. The
National Electric Code has the following to say regarding connection of attachment
plugs…
Article 406.6 (B) Connection of Attachment Plugs
Attachment plugs shall be installed so that their prongs, blades, or pins are not
energized unless inserted into an energized receptacle or cord connectors. No
receptacle shall be installed so as to require the insertion of an energized attachment
plug as its source of supply.
So, this type of connection is illegal and has the potential to kill you…
(Thanks Millerized for helping to keep me safe!)
In addition to everything mentioned above, I authored a set of startup instructions for
the system in the event that I am not home for any other adult to utilize. These are
stored in an easy to access location on our main floor.
Stay safe and remember, when in doubt, call a professional!