5/19/2014 CR4 - Thread: Knee Point Voltage and Current Transformers http://cr4.globalspec.com/thread/43832/Knee-Point-Voltage-and-Current-Transformers 1/3 #1 #2 In reply to #1 #3 In reply to #2 Sites: GlobalSpec.com | GlobalSpec Electronics | CR4 | Electronics360 Previous in Forum: UPS Rating and Capacity Next in Forum: Generator Life Expectancy B.JEYACHANDRAN Active Contributor Join Date: Apr 2009 Location: Madurai Posts: 22 Knee Point Voltage and Current Transformers 09/23/2009 10:22 AM dear friend, kindly any one explaine me what is the effect of knee point voltage in CT. If one PX Class CT having Vk>300V, Ia<30 mA how i calculate this CT BURDEN also what is the primary current when th ct is satsurated, thanking you, yours , B.JEYACHANDRAN Interested in this topic? By joining CR4 you can "subscribe" to this discussion and receive notification when new comments are added. Join CR4, The Engineer's Place for News and Discussion! Manimaran Vasan Member Join Date: Sep 2009 Location: ABB Limited, Nashik Posts: 9 Re: Knee Point Voltage and Current Transformers 09/26/2009 2:26 AM Dear friend, Knee Point voltage is nothing but a point at which the CT saturates. Thatsy its always better to design the CTs which can operate without saturation even at a voltage appears in the CT during fault condition. Pls find below the following formula for calculating the Knee point voltage. Vk=2If(Rc t+2Rl). where, If is the current refected to the CT secondary during fault condition, Rct is the resistance of the CT which can be adopted by means of a thumb rule considering the CT ratio, Rl is the lead resistance i.e. sum of the resistance of the wire connected between the relay & CT and Impedance offered by the internal circuitary of the relay For PS class CT's designed considering the above,burden is not applicable. Pls revert back if you have any further queries. Regards, Manimaran.V B.JEYACHANDRAN Active Contributor Join Date: Apr 2009 Location: Madurai Posts: 22 Re: Knee Point Voltage and Current Transformers 09/26/2009 2:42 AM dear friend, thank you for your guidence, how i calculate the fault current limit in primary side with knee point voltage Manimaran Vasan Member Join Date: Sep 2009 Location: ABB Limited, Nashik Posts: 9 Re: Knee Point Voltage and Current Transformers 09/26/2009 7:44 AM Dear Friend, Pls find below the formula for calculating the fault current, Fault current(in KA) = Rated Curent/(% Impedance*1000) % Impedence shall be calculated for the system from the point of source to the point of occurence of the fault. The Engineer's Place for News and Discussion ® Login | Register

Upload: jhakg169712275

Post on 28-Dec-2015

31 views

Category:

Documents


0 download

TRANSCRIPT

Page 1: CR4 - Thread_ Knee Point Voltage and Current Transformers

5/19/2014 CR4 - Thread: Knee Point Voltage and Current Transformers

http://cr4.globalspec.com/thread/43832/Knee-Point-Voltage-and-Current-Transformers 1/3

#1

#2In reply to #1

#3In reply to #2

Sites: GlobalSpec.com | GlobalSpec Electronics | CR4 | Electronics360

Previous in Forum: UPS Rating and Capacity Next in Forum: Generator Life Expectancy

B.JEYACHANDRANActive Contributor

Join Date: Apr 2009Location: MaduraiPosts: 22

Knee Point Voltage and Current Transformers09/23/2009 10:22 AM

dear friend,

kindly any one explaine me what is the effect of knee point voltage in CT.

If one PX Class CT having Vk>300V, Ia<30 mA how i calculate this CT BURDEN also what is the primary current whenth ct is satsurated,

thanking you,

yours ,

B.JEYACHANDRAN

Interested in this topic? By joining CR4 you can "subscribe" tothis discussion and receive notification when new comments are added.

Join CR4, The Engineer's Place for News and Discussion!

ManimaranVasanMember

Join Date: Sep 2009Location: ABB Limited,NashikPosts: 9

Re: Knee Point Voltage and Current Transformers09/26/2009 2:26 AM

Dear friend,

Knee Point voltage is nothing but a point at which the CT saturates. Thatsy its always better to design the CTs whichcan operate without saturation even at a voltage appears in the CT during fault condition. Pls find below the followingformula for calculating the Knee point voltage.

Vk=2If(Rct+2Rl).

where, If is the current refected to the CT secondary during fault condition,

Rct is the resistance of the CT which can be adopted by means of a thumb rule considering the CT ratio,

Rl is the lead resistance i.e. sum of the resistance of the wire connected between the relay & CT and Impedanceoffered by the internal circuitary of the relay

For PS class CT's designed considering the above,burden is not applicable.

Pls revert back if you have any further queries.

Regards,

Manimaran.V

B.JEYACHANDRANActive Contributor

Join Date: Apr 2009Location: MaduraiPosts: 22

Re: Knee Point Voltage and Current Transformers09/26/2009 2:42 AM

dear friend,

thank you for your guidence, how i calculate the fault current limit in primary side with knee point voltage

ManimaranVasanMember

Join Date: Sep 2009Location: ABB Limited,NashikPosts: 9

Re: Knee Point Voltage and Current Transformers09/26/2009 7:44 AM

Dear Friend,

Pls find below the formula for calculating the fault current,

Fault current(in KA) = Rated Curent/(% Impedance*1000)

% Impedence shall be calculated for the system from the point of source to the point of occurence of the fault.

The Engineer's Place for News and Discussion® Login | Register

Page 2: CR4 - Thread_ Knee Point Voltage and Current Transformers

5/19/2014 CR4 - Thread: Knee Point Voltage and Current Transformers

http://cr4.globalspec.com/thread/43832/Knee-Point-Voltage-and-Current-Transformers 2/3

#4In reply to #3

#5In reply to #3

#12In reply to #1

#6

#7In reply to #6

#8In reply to #7

#9In reply to #8

#11In reply to #9

#10

Regards,

Manimaran.V

shock007Active Contributor

Join Date: Jun 2008Posts: 10

Re: Knee Point Voltage and Current Transformers09/28/2009 4:12 AM

Dear Manimaran,

Can you please explain, how to calculate Ia and what is its significance?

AnonymousPoster

Re: Knee Point Voltage and Current Transformers09/28/2009 11:19 AM

dear friend,

thankyou friend

AnonymousPoster #1

Re: Knee Point Voltage and Current Transformers05/29/2012 1:48 AM

ayubksebMember

Join Date: Apr 2008Location: Doha QatarPosts: 8

Re: Knee Point Voltage and Current Transformers09/30/2009 12:38 PM

Dear member

For PX class CTs , the burden is not normally mentioned . There the CT is defiened based on the CT kneepoint voltage ,magnetising current etc . The burden is mentioned in class P CTs

In PX class CTs the kneepoint voltage is normally based on the max fault current and a diamensioning factor based onsystem X/R ratio

Ayub

shock007Active Contributor

Join Date: Jun 2008Posts: 10

Re: Knee Point Voltage and Current Transformers09/30/2009 9:06 PM

Understand from above formula to calculate knee point voltage. Can you please explain how to calculate magnetisingcurrent.

ayubksebMember

Join Date: Apr 2008Location: Doha QatarPosts: 8

Re: Knee Point Voltage and Current Transformers10/01/2009 12:24 AM

There is no formulae as such for calculating the magnetising current . However some a application demands minimumvalue of mag current for relay setting ( eg; REF protection ). Iin any case a magnetising current of less than 30 mAwould be sufficient for most of the application

ManimaranVasanMember

Join Date: Sep 2009Location: ABB Limited,NashikPosts: 9

Re: Knee Point Voltage and Current Transformers10/01/2009 3:31 AM

ya.. thats right.. there is no formula for calculating magnetising current. however, lesser the magnetising current,better is your CT performance.

Regards,

Manimaran.V

GovindarulParticipant

Join Date: May 2012Posts: 2

Re: Knee Point Voltage and Current Transformers05/07/2012 7:57 AM

The formula for calulating the required magnetising current for the CT =

[(IOP / CT Ratio) - IR] / n

Where,

IOP = Relay operating current (absolute current value in terms of CT primary)

IR = Relay setting current (in terms of CT secondary)

n = Number of parallel CTs forming (87) protected zone

Anonymous Re: Knee Point Voltage and Current Transformers06/20/2010 6:35 AM

Page 3: CR4 - Thread_ Knee Point Voltage and Current Transformers

5/19/2014 CR4 - Thread: Knee Point Voltage and Current Transformers

http://cr4.globalspec.com/thread/43832/Knee-Point-Voltage-and-Current-Transformers 3/3

#13In reply to #10

Copy to Clipboard

Poster

Govindarul Re: Knee Point Voltage and Current Transformers05/29/2012 2:01 AM

Register to Reply 13 comments

Back to top

Interested in this topic? By joining CR4 you can "subscribe" tothis discussion and receive notification when new comments are added.

Join CR4, The Engineer's Place for News and Discussion!

Users who posted comments:

Anonymous Poster (3); ayubkseb (2); B.JEYACHANDRAN (1); Govindarul (2); Manimaran Vasan (3); shock007 (2)

Previous in Forum: UPS Rating and Capacity Next in Forum: Generator Life Expectancy

You might be interested in: Voltage Dividers and Voltage References, Display and Point of Purchase Services (POP), Voltage Converters andVoltage Inverters

"Twenty years from now you will be more disappointed by the things that you didn't do than by the ones you did do. So throw off thebowlines. Sail away from the safe harbor. Catch the trade winds in your sails. Explore. Dream. Discover." -- Mark Twain

All times are displayed in US/Eastern (EDT) (Register to change time zone)

©2014 IHS.No part of this site may be copied, transmitted or stored, in any form or by any means, without prior written permission ofIHS. The information contained on this site is by users for users and is provided for information purposes only and does notconstitute advice. Any views or opinions expressed by users are personal to them and do not represent the views oropinions of IHS. You should check any information and use your own judgment or seek expert advice before doing or notdoing anything on the basis of what you read here. IHS does not verify or warrant the accuracy or completeness of anyinformation on this site and, to the extent permitted by law, IHS shall not be liable for any loss, damage or expense incurredby reliance on it or for any dealings you have with users or other third parties that take place using or facilitated by this site.