bacnet forum london 2011

38
Increasing the Value of Properties with BACnet Successful Interoperability and Building Systems Integration 13 April 2011 LONDON Frank Neudecker Thermokon Sensortechnik GmbH The wireless extension to BACnet The battery-less wireless EnOcean Standard including Case Studies with EnOcean - BACNet

Upload: neudecker

Post on 25-May-2015

717 views

Category:

Technology


8 download

DESCRIPTION

Presentation held on behalf of EnOcean Alliance during the 2011 BACnet forum in London

TRANSCRIPT

Page 1: BACnet Forum London 2011

Increasing the Value of Properties with BACnet

Successful Interoperability and Building Systems Integration

13 April 2011 LONDON

Frank NeudeckerThermokon Sensortechnik GmbH

The wireless extension to BACnetThe battery-less wireless EnOcean Standard including Case Studies with EnOcean - BACNet

Page 2: BACnet Forum London 2011

Companylogo

•Battery less rf-technology (EnOcean)

•EnOcean – BACnet Products & Systems

•Reference Projects

•BACnet-EnOcean Cooperation

EnOcean & BACnet – a smart combination

Thermokon Sensortechnik GmbH | Frank Neudecker Page 2

Page 3: BACnet Forum London 2011

Companylogo

Energy Conservation Requirement

Buildings Use 40% of our Total

Energy Requirements

In 2030 the Global Electrical Power

Demand will be 2 x that of 2003

Increase use of Fossile energy ?

Nuclear power ?

Thermokon Sensortechnik GmbH | Frank Neudecker Page 3

Page 4: BACnet Forum London 2011

Companylogo

Thermokon Sensortechnik GmbH | Frank Neudecker Page 4

Energy Conservation in BuildingsBuiding Envelope

Insulation, Windows, Doors, etc.

Energy Savings 20-60%

Expensive / Invasive in retrofit scenario

ROI 10 – 30 years typically

Equipment Modernization

New HVAC etc.

Energy Savings 10-30%

ROI 5 – 15 years typically

Building Automation Systems

Sensors, switches etc.

Energy Savings 20-30%

Low invest, non-invasive (retrofit)

ROI 1 – 5 years typically

Page 5: BACnet Forum London 2011

Companylogo

High Performance Buildings

• High Performance Buildings require Building Automation Systems

• To enable up to 30% energy savings

• To do this Sensors are required e.g. – Occupancy

– Lighting levels

– Temperature / Humidity / CO2

– Door / Window Status

Thermokon Sensortechnik GmbH | Frank Neudecker Page 5

Page 6: BACnet Forum London 2011

Companylogo

Wiring: Expensive & Invasive

Conventional Wired Solutions

– Time-Consuming

– Building Mess & Noise

– Inflexible

– Invasive

– Expensive Over Building Lifespan

Thermokon Sensortechnik GmbH | Frank Neudecker Page 6

Page 7: BACnet Forum London 2011

Companylogo

wireless, no batteries

0..10V, relay out

Ethernet, RS485

DDC

USB

Thermokon Sensortechnik GmbH | Frank Neudecker Page 7

Page 8: BACnet Forum London 2011

Companylogo

Thermokon Sensortechnik GmbH | Frank Neudecker Page 8

Wireless Transmission Considerations

• Frequency

– use license free-band.

• Range

– lower frequency, longer range.

– ensure receiver within safe range.

– take attenuators/angles into account

• Attenuators

– metal & concrete absorb/block most signals

– other materials reduce signal range

Page 9: BACnet Forum London 2011

Companylogo

Page 9

Problems when using Batteries

• Using batteries does result in

– maintenance

– Stocking of batteries

– Monitoring battery status

– Time /labout to replace batteries

– Waste disposal

Battery failure = sensor failure XThermokon Sensortechnik GmbH | Frank Neudecker

Page 10: BACnet Forum London 2011

Companylogo

Page 10

Solution: Energy harvesting rf sensors

„No Wires. No Batteries. No Limits“

Thermokon Sensortechnik GmbH | Frank Neudecker

Page 11: BACnet Forum London 2011

Companylogo

Page 11

Products using mechanical Harvester

Thermokon Sensortechnik GmbH | Frank Neudecker

Page 12: BACnet Forum London 2011

Companylogo

• Rf module (STM 110)

• Plug and Play Sensor module

» Gold Cap storing excessive energy

» Timer

» Signal conditioning and acquisition

» Rf transmission

• „Ultra Low Power“ Design, i.e. sleep timer consuming 20 nA only

• 3 - 7 days coninous operation in absolute darkness with fully charged Gold Cap

Solar energy

Thermokon Sensortechnik GmbH | Frank Neudecker Page 12

Page 13: BACnet Forum London 2011

Companylogo

Page 13

Solar energy: typical products

Thermokon Sensortechnik GmbH | Frank Neudecker

Page 14: BACnet Forum London 2011

Companylogo

Thermokon Sensortechnik GmbH | Frank Neudecker Page 14

Body Temperature Powers rf-sensor

Temperature difference between heating pipe and ambient powers valve actuator

Thermal energy: demo unit

Page 15: BACnet Forum London 2011

Companylogo

Thermokon Sensortechnik GmbH | Frank Neudecker Page 15

Space control with EnOcean Sensors

Room-controller

Lighting i.e. using DALI

Air condition

Shadingi.e. through SMI

Page 16: BACnet Forum London 2011

Companylogo

Page 16

EnOcean – BACnet Gateways / Controllers

Thermokon Sensortechnik GmbH | Frank Neudecker

Page 17: BACnet Forum London 2011

Companylogo

Page 17

BACnet-solution with EnOcean-sensors

Thermokon Sensortechnik GmbH | Frank Neudecker

Page 18: BACnet Forum London 2011

Companylogo

Thermokon Sensortechnik GmbH | Frank Neudecker Page 18

Calculation of Installation Time Savings

Assumptions:• 2.8 minutes installation time average per 1 meter cable• Approx. 1,8 meter cable per m2 office space (lights & shading)• Approx. 2,5 meter cable per m2 office space (lights & shading & room temperature)

source ZVEH (German Electricians Union)

ApplicationLights & Shading

Lights & Shading & Room Temp.  

Office Area in m2

Time Savings in Hours

Savings in Man Days

5.000 408 583 51 - 73

10.000 817 1167 102 - 146

20.000 1633 2333 204 – 292

50.000 4083 5833 510 - 729

Page 19: BACnet Forum London 2011

Companylogo

Thermokon Sensortechnik GmbH | Frank Neudecker Page 19

Storebrand Eiendom, Oslo, N

• SRC65 Bacnet receivers• SR06 & SR07P room temp.sensors• SR04 rh to calculate dew point • 8 repeaters (2nd Level)• Chilled floor / ceiling

Page 20: BACnet Forum London 2011

Companylogo

Thermokon Sensortechnik GmbH | Frank Neudecker

Promutuel Insurance Building Quebec, CA

Page 20

>800 battery-less wireless modules connected to BACnet building automation system

LEED Gold Certification

Savings in each building

80% Initial Installation Costs

Lighting & HVAC Energy Costs

Page 20

Page 21: BACnet Forum London 2011

Companylogo

Thermokon Sensortechnik GmbH | Frank Neudecker

St. Joseph´s School, Lacoll, Quebec, CA

• Individual Room Temperature Control

• Retrofit during normal school operation

• Connected via BACnet / Internet for remote monitoring & controlling

•Savings– 30% HVAC Energy Costs– ROI less than 2 years

Page 21

Page 22: BACnet Forum London 2011

Companylogo

Thermokon Sensortechnik GmbH | Frank Neudecker

Glumac “Office of the Future”, Irvine, CA

New Construction – LEED Platinum

Occupancy based Lighting & HVAC Controls for energy savings (> 75% better than Title 24)

Flexible for varying office space usage

EnOcean Wireless - BACnet Solution

Page 22

Page 23: BACnet Forum London 2011

Companylogo

Thermokon Sensortechnik GmbH | Frank Neudecker Page 23

DSM-RTR

RUBI

DAC-322

Receivers / Repeaters

Thermostats

Gas HeatersGarage Doors Contact Sensor

Targray Headquarters, Kirkland, QC, CA

Page 24: BACnet Forum London 2011

Companylogo

Staatsbibliothek Berlin, Germany

• Refurbishment of building 2

• Wireless room temperature sensors

• 130 rooms interfacing the existing Messner (TAC – Schneider Electric) controller

Thermokon Sensortechnik GmbH | Frank Neudecker Page 24

Page 25: BACnet Forum London 2011

Companylogo

Thermokon Sensortechnik GmbH | Frank Neudecker Page 25

Hospital: Institut de Cardiologie, Montreal, CA

Page 26: BACnet Forum London 2011

Companylogo

Thermokon Sensortechnik GmbH | Frank Neudecker Page 26

ORCAwebORCAview

Triac Baseboard Relays

Thermostats

Switches Lighting Relays

AC Unit

/ IP

RUBI

Antenna(3x)

DHMI

Motion Sensors

Photo sensors

Office Building, Montreal, CA

Page 27: BACnet Forum London 2011

Companylogo

Page 27

IKEA’s North American Distribution Center, CA

• HVAC Retrofit – Comfort & Energy

• Savings (30%)

• 4 Buildings @ 60.000m2

• EnOcean Batteryless / Wireless Sensors

• BACnet System

Thermokon Sensortechnik GmbH | Frank Neudecker

Page 28: BACnet Forum London 2011

Companylogo

Page 28

DSC-1212ERUBI

Controller

HeaterHeating

UnitsThermostat

Intranet Client

Antenna

Repeater Relay

IKEA Distribution Center, Brossard, CA

Thermokon Sensortechnik GmbH | Frank Neudecker

Page 29: BACnet Forum London 2011

Companylogo

Three Rivers Technology Park, Quebec, CA

New Construction

Occupancy based / dimmable Lighting & HVAC Controls for energy savings

EnOcean Wireless - BACnet Solution

Thermokon Sensortechnik GmbH | Frank Neudecker

Page 30: BACnet Forum London 2011

Companylogo

Thermokon Sensortechnik GmbH | Frank Neudecker Page 30

O2 New Office Building, Slough, 2010

• 3 buildings / 7 floors

• 100 control zones per floor

• 64 EnOcean receivers

• 560 EnOcean switches

• 5800 DALI Luminaries

• All switches used on/off and dimming

Page 31: BACnet Forum London 2011

Companylogo

Thermokon Sensortechnik GmbH | Frank Neudecker

Barclays Bank – Energy Saving Retrofit

Page 31

Page 32: BACnet Forum London 2011

Companylogo

„The Squaire“ Frankfurt Airport 2011

2000 feet long building „Air-Rail Center“

2 Hotels (Hilton)

Business Center

Railway Station & Travel Center

Offices

Shopping area

12.000 Battery-less Wireless Switches and Sensors for Lighting & HVAC Control

Thermokon Sensortechnik GmbH | Frank Neudecker Page 32

Page 33: BACnet Forum London 2011

Companylogo

Historical, Sports, Governmental,…No Limits

Thermokon Sensortechnik GmbH | Frank Neudecker Page 33

Page 34: BACnet Forum London 2011

Companylogo

Thermokon Sensortechnik GmbH | Frank Neudecker Page 34

BACnet – EnOcean Alliance Cooperation

“The task at hand is to define common implementation rules for an EnOcean/BACnet gateway,” said Dave Robin, Chairman of the BACnet Technical Working Group. “This will entail a number of issues, including specifying the network topology and the BACnet/EnOcean objectives needed to define a single model so that all implementations will be interoperable.”

“The world has evolved towards a wired and wireless infrastructure, and it is a significant step to bridge these together with a standard mechanism for building automation suppliers and users,” said Andy McMillan, President of BACnet International

Page 35: BACnet Forum London 2011

Companylogo

BACnet – EnOcean Alliance Cooperation

• BACnet Wireless Networking Working Group BACnet_WN-WG

• Chairman – Jerry Martocci – Johnson Controls Inc.

• Work Item started in Q1 2010

• Developing specification for a BACnet to EnOcean Gateway Standard

• Target: ANSI/ASHRAE SSPC135 Standard (BACnet) – as “Best Practices”

• Yahoo group “BACnet_WN-WG” http://tech.groups.yahoo.com/group/BACnet_WN-WG/

Thermokon Sensortechnik GmbH | Frank Neudecker Page 35

Page 36: BACnet Forum London 2011

Companylogo

Thermokon Sensortechnik GmbH | Frank Neudecker Page 36

EnOcean Alliance

• Establishing the EnOcean-Technology as the international Standard for sustainable, energy efficient buildings

• Promotion of a wide spectrum of interoperable products

• Safeguarding the interoperability of EnOcean products

• Definition of new EEPs

Page 37: BACnet Forum London 2011

Companylogo

The EnOcean Standard

• > 170 companies supporting (Apr`11)

• > 700 interoperable products

• >> 100,000 buildings deployed

• IEC Standardization ongoing

• The only Wireless Standard developed for and capable of energy harvesting operation

• Thermokon: ~200.000 devices deployed since 2003

Thermokon Sensortechnik GmbH | Frank Neudecker Page 37

Page 38: BACnet Forum London 2011

Companylogo

– EnOcean Alliance– 2400 Camino Ramon, Suite 375– San Ramon, CA 94583– USA

– Phone US: +1.925.275-6601– Phone Germany:

+49.6172.997 879– [email protected] – www.enocean-alliance.org

Thermokon Sensortechnik GmbH | Frank Neudecker Page 38

Thank You !