2008-11-17 tall building forum - mep session (gz west tower)

36
17 November 2008 Tall Building Forum Tall Building Forum – MEP Session Guangzhou West Tower

Upload: catherine-chen

Post on 27-Apr-2015

181 views

Category:

Documents


2 download

TRANSCRIPT

Page 1: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

17 November 2008

Tall Building Forum

Tall Building Forum – MEP Session Guangzhou West Tower

Page 2: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

MEP Session – Guangzhou West Tower

MEP Design Consideration for

Tall Buildings

Tall Building Forum – MEP Session Guangzhou West Tower

By Calvin Fu / Tom Cheung

Page 3: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

1. Introduction

2. MEP Design Considerations for Tall Buildings2.1 MEP Services Zone Impact on Floor-to-floor height2.2 Core Efficiency2.3 Ratio of Total Plant Room Area (TPRA) and Typical Floor Area

(TFA) to Gross Floor Area (GFA)2.4 MEP System for Composite Building2.5 Centralized vs De-centralized System

Agenda

Tall Building Forum – MEP Session Guangzhou West Tower

3. Summary

Page 4: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

Tall Building Forum – MEP Session Guangzhou West Tower

Introduction

Page 5: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

• West Tower is located in Guangzhou Zhujiang New Town with approx. 40,000m² Gross Area

• 103 Storey with approx. 432m height

1.0 Introduction

• Composite building which consists of multi-functional areas such as office, hotel, retails, carpark, etc.

Tall Building Forum – MEP Session Guangzhou West Tower

Page 6: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

Tall Building Forum – MEP Session Guangzhou West Tower

MEP Design Considerations for Tall Buildings

Page 7: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

Tall Building Forum – MEP Session Guangzhou West Tower

Page 8: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

• Floor-to-floor height and clear headroom are bounded by the structural MEP (SMEP) zone

2.1 MEP Services

Zone Impact

STR

MEP

Tall Building Forum – MEP Session Guangzhou West Tower

• Minimize the required height of SMEP zone in turn of increasing the total number of floors with a limited height

• Intensive design coordination is required to achieve optimized design

Page 9: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

MEP Services Zone Coordination2.1 MEP Services

Zone Impact

Electrical Trunking

ELV TrunkingExhaust

Tall Building Forum – MEP Session Guangzhou West Tower

CorridorTypical Clear Headroom:

2800 - 3300mm

Intake Airduct

Emergency Trunking Cable

Tray

Trunking TrunkingExhaust Airduct Sprinkler

Pipe

Typical Floor-to-Floor Height:

4000 - 4500mm

Page 10: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

Comparison of Different System

3900mm Floor HeightFCU System

Fit-in RC

Ribbed Slab System

Fit-in Pre-stress

Flat Slab System

Fit-in Composite

Beam / Slab SystemRC

3900mm Floor Height 3900mm Floor Height

Flat Slab

2.1 MEP Services

Zone Impact

Tall Building Forum – MEP Session Guangzhou West Tower

VAV System

Underfloor AC Supply System

3900mm Floor Height4000mm Floor Height4000mm Floor Height

4000mm Floor Height 4000mm Floor Height 4000mm Floor Height

Composite Beam

Page 11: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

Headroom Summary Table

ProjectFL-FL Height (mm)

Clear Headroom

(mm)

SMEP-FL Ratio

1 Guangzhou West Tower 4500 3100 0.31

2 Shanghai China Merchant Bank 4500 3000 0.33

3 Beijing CCTV Headquaters (Main Tower) 4250 2800 0.34

4 Shenzhen Stock Exchange 4350 2900 0.33

2.1 MEP Services

Zone Impact

Tall Building Forum – MEP Session Guangzhou West Tower

5 HWP Tianjin Complex 4200 3000 0.29

6 Suzhou Gate to the East 4000 2620 0.35

7 Guangzhou R & F Mixed-Use Tower 4200 2600 0.38

8 Hong Kong Nina Tower 3850 2650 0.31

9 Chongqing World Finance Tower 4200 2800 0.33

10 Shenzhen Kingkey Finance Tower 4200 2800 0.33

Remarks: SMEP-FL denotes structural MEP zone height to floor height.

Page 12: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

Tall Building Forum – MEP Session Guangzhou West Tower

Page 13: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

• Lift core is the major element occupied the core area of tall building

2.2 Core

EfficiencyLift System

• Different lift design strategy will be considered for optimizing the core efficiency: -

� Using high speed lift

� Sky lobby

� Use of double-deck lift

Tall Building Forum – MEP Session Guangzhou West Tower

� Use of double-deck lift

Page 14: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

• Study of Grade A Office Portion

1. Conventional Option

2. Sky Lobby Option with Single-Deck Shuttle Lift

3. Sky Lobby Option with Double-Deck Shuttle Lift

Lift Traffic Analysis Comparison2.2 Core

Efficiency

Single-Deck Lift

Sky Lobby

Sky Lobby

Tall Building Forum – MEP Session Guangzhou West Tower

Double-Deck

Shuttle Lift

Single-Deck

Shuttle Lift

Page 15: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

Option 1 Option 2 Option 3

No. of Lifts 36 42 40

Lift Traffic Analysis Comparison

• Summary

2.2 Core

Efficiency

Tall Building Forum – MEP Session Guangzhou West Tower

Min. No. of

Escalators0 0 4

No. of Lift

Shafts36 24 22

Lift Shaft Volume (m3)

40,000 28,000 26,500

Page 16: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

West Tower Lift System2.2 Core

Efficiency

Sky

Local Lift

Tall Building Forum – MEP Session Guangzhou West Tower

• Double-deck shuttle lifts are applied for low and high zone on office portion of building

• 2 sky lobbies for office shuttle lifts

• 1 sky lobby for hotel shuttle lifts

• Local lifts as inter-floor transfer

Shuttle Lift

Sky Lobby

Page 17: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

Other MEP Services Inside Core

ELV

ELV

Electrical

FS

FS

Staircase Pressurization

Smoke Extraction

HVAC

PD

Floor Efficiency ~71%

2.2 Core

Efficiency

Tall Building Forum – MEP Session Guangzhou West Tower

ElectricalELV

ELV

Electrical

FS

FS

Staircase Pressurization

Smoke Extraction

Smoke Extraction

HVAC

PD

Page 18: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

Core Efficiency Summary Table2.2 Core

Efficiency

ProjectBuilding Height

(m)

Core Efficiency

(%)

1 Guangzhou West Tower 432 71

2 Shanghai China Merchant Bank 200 74

3 Beijing CCTV Headquaters (Main Tower) 234 72

4 Shenzhen Stock Exchange 240 71

Tall Building Forum – MEP Session Guangzhou West Tower

5 HWP Tianjin Complex 246 75

6 Suzhou Gate to the East 280 74

7 Guangzhou R & F Mixed-Use Tower 285 74

8 Hong Kong Nina Tower 320 72

9 Chongqing World Finance Tower 402 77

10 Shenzhen Kingkey Finance Tower 439 70

Page 19: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

Tall Building Forum – MEP Session Guangzhou West Tower

Page 20: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

• Electrical

� Power Substation (Tx room, Switchroom)

� Backup Generator

� Lift Machine Room

� Security Control Room

� Fire Services Control Room

• Mechanical

MEP Plant Space Category2.3 Ratio of TPRA

and TFA to GFA

Tall Building Forum – MEP Session Guangzhou West Tower

• Mechanical

� Chiller Plant Room

� Cooling Tower

� Potable & Flushing Water Tank and Pump

Room

� Fire Services Water Tank and Pump Room

� Smoke Extraction & Staircase Pressurization

Room

Page 21: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

Plantroom Allocation2.3 Ratio of TPRA

and TFA to GFA

Hotel ChillerAHU

Fan RoomPAUFan Room

PAU + Free Cooling FanAHUFan RoomPressurization fan & smoke extraction fan roomFS Tank

Hotel Cooling Tower

Sprinkler Water TankPotable Water TankLife Machine RoomSmoke Extraction (Atrium)PAU & AHU

Fan RoomBoiler Room

PAUAHUSmoke Extraction(Atrium)

P&D TransferAHU / Fan RoomPotable Water

Tall Building Forum – MEP Session Guangzhou West Tower

ChillerChilled Water PumpMain TX RoomGeneratorPotable WaterFS

Fan RoomLife Machine RoomSwimming Pool Filtration PlantTX Room

Fan Room

Pressurization fan & smoke extraction fan roomTX RoomPotable WaterFS Tenant Heat Rejection PAU + AHU

EAFPressurization fan & smoke extraction fan roomPotable WaterFSTX RoomHX + Chilled Water PumpTenant Heat Rejection

Page 22: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

Total Plant Space Summary Table

ProjectTFA –GFA

Ratio (%)

TPRA –GFA Ratio

(%)

1 Guangzhou West Tower 1.12 10.50

2 Shanghai China Merchant Bank 1.69 10.89 ~11%

2.3 Ratio of TPRA

and TFA to GFA

Tall Building Forum – MEP Session Guangzhou West Tower

3 Shenzhen Stock Exchange 1.66 10.46

4 Guangzhou R & F Mixed-Use Tower 1.26 10.23

5 Chongqing World Finance Tower 1.15 11.09

Remarks:

1. TFA-GFA denotes typical floor area to GFA.

2. TPRA-GFA denotes total plant room area to GFA.

Page 23: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

Tall Building Forum – MEP Session Guangzhou West Tower

Page 24: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

• Example

2.4 MEP System

for Composite

Building

Architectural Zoning

Zone A: Executive

Office

Zone B: Hotel

Tall Building Forum – MEP Session Guangzhou West Tower

Zone C: Office

Zone E: Car Park

Zone D: Retail

Page 25: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

• LV Power Distribution System

MEP Functional Zoning

Zone A: Executive

Office Zone B: Hotel

Zone AZone B

2.4 MEP System

for Composite

Building

Tall Building Forum – MEP Session Guangzhou West Tower

Architectural Zoning

Zone C: Office

Zone E: Car Park

MEP Zoning

Zone C

Zone DZone D: Retail

Page 26: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

• HVAC System

MEP Functional Zoning

Zone A: Executive

Office Zone B: Hotel

Zone BZone A

2.4 MEP System

for Composite

Building

Tall Building Forum – MEP Session Guangzhou West Tower

Architectural Zoning

Zone C: Office

Zone E: Car Park

Zone D: Retail

MEP Zoning

Zone C

Page 27: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

• Lift System

MEP Functional Zoning

Zone A: Executive

Office Zone B: Hotel

Zone BZone A

2.4 MEP System

for Composite

Building

Tall Building Forum – MEP Session Guangzhou West Tower

Architectural Zoning

Zone C: Office

Zone E: Car Park

MEP Zoning

Zone C

Zone D

Zone E

Zone D: Retail

Page 28: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

2.4 MEP System

for Composite

Building

West Tower Zoning Arrangement

Zone 3: Office

Zone 4: Hotel

Refuge / ME 4

Zone 3: Hotel

Zone 2: OfficeRefuge

ME5

Tall Building Forum – MEP Session Guangzhou West Tower

MEP Zoning for LV DistributionArchitectural Zoning

Zone 1: Suite Office,

Podium, Carpark

Zone 2: Basement

Chiller Plant

Zone 1: Retails,

Basement, Carpark

Refuge / ME 1

Refuge / ME 2

Refuge / ME 3

Page 29: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

Tall Building Forum – MEP Session Guangzhou West Tower

Page 30: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

2.5 Centralized vs

De-centralized

System

• For super tall building, composite zoning is normally adopted

• Centralized System

� Fire Services System

� Plumbing System

� Security System

System Arrangement

Tall Building Forum – MEP Session Guangzhou West Tower

• De-centralized System

� Air-conditioning System

� Power Supply System

� Lift System

Page 31: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

2.5 Centralized vs

De-centralized

System

Centralized AHU System

• Located at one or more specified floors

Pros: -

• No AHU at typical floor - increase core efficiency of typical floor

• Centralized maintenance works

Tall Building Forum – MEP Session Guangzhou West Tower

• Centralized maintenance works

Cons: -

• More plant space requires at podium area and main entrance floor

• Duct-borne noise is existed

Page 32: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

2.5 Centralized vs

De-centralized

System

De-centralized AHU System

• Located at each typical floor

Pros: -

• Better individual AC control

• High availability for equipment selection

• Less plant space required at

Tall Building Forum – MEP Session Guangzhou West Tower

• Less plant space required at podium area and main entrance floor

Cons: -

• Reduce core efficiency of typical floor

• More individual maintenance work

Page 33: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

2.5 Centralized vs

De-centralized

System

West Tower AHU System

AHU on each floor

AHU on each floor

Tall Building Forum – MEP Session Guangzhou West Tower

De-centralized AHU System in GZ West Tower

Page 34: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

Tall Building Forum – MEP Session Guangzhou West Tower

Summary

Page 35: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

MEP Design Considerations for Tall Buildings

- MEP Services Zone Impact on Floor-to-floor height

- Core Efficiency

- Ratio of Total Plant Room Area (TPRA) and Typical Floor Area (TFA)

3.0 Summary

Tall Building Forum – MEP Session Guangzhou West Tower

- Ratio of Total Plant Room Area (TPRA) and Typical Floor Area (TFA)

to Gross Floor Area (GFA)

- MEP System for Composite Building

- Centralized vs De-centralized System

Page 36: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)

Tall Building Forum – MEP Session Guangzhou West Tower