2008-11-17 tall building forum - mep session (gz west tower)
TRANSCRIPT
![Page 1: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/1.jpg)
17 November 2008
Tall Building Forum
Tall Building Forum – MEP Session Guangzhou West Tower
![Page 2: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/2.jpg)
MEP Session – Guangzhou West Tower
MEP Design Consideration for
Tall Buildings
Tall Building Forum – MEP Session Guangzhou West Tower
By Calvin Fu / Tom Cheung
![Page 3: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/3.jpg)
1. Introduction
2. MEP Design Considerations for Tall Buildings2.1 MEP Services Zone Impact on Floor-to-floor height2.2 Core Efficiency2.3 Ratio of Total Plant Room Area (TPRA) and Typical Floor Area
(TFA) to Gross Floor Area (GFA)2.4 MEP System for Composite Building2.5 Centralized vs De-centralized System
Agenda
Tall Building Forum – MEP Session Guangzhou West Tower
3. Summary
![Page 4: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/4.jpg)
Tall Building Forum – MEP Session Guangzhou West Tower
Introduction
![Page 5: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/5.jpg)
• West Tower is located in Guangzhou Zhujiang New Town with approx. 40,000m² Gross Area
• 103 Storey with approx. 432m height
1.0 Introduction
• Composite building which consists of multi-functional areas such as office, hotel, retails, carpark, etc.
Tall Building Forum – MEP Session Guangzhou West Tower
![Page 6: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/6.jpg)
Tall Building Forum – MEP Session Guangzhou West Tower
MEP Design Considerations for Tall Buildings
![Page 7: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/7.jpg)
Tall Building Forum – MEP Session Guangzhou West Tower
![Page 8: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/8.jpg)
• Floor-to-floor height and clear headroom are bounded by the structural MEP (SMEP) zone
2.1 MEP Services
Zone Impact
STR
MEP
Tall Building Forum – MEP Session Guangzhou West Tower
• Minimize the required height of SMEP zone in turn of increasing the total number of floors with a limited height
• Intensive design coordination is required to achieve optimized design
![Page 9: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/9.jpg)
MEP Services Zone Coordination2.1 MEP Services
Zone Impact
Electrical Trunking
ELV TrunkingExhaust
Tall Building Forum – MEP Session Guangzhou West Tower
CorridorTypical Clear Headroom:
2800 - 3300mm
Intake Airduct
Emergency Trunking Cable
Tray
Trunking TrunkingExhaust Airduct Sprinkler
Pipe
Typical Floor-to-Floor Height:
4000 - 4500mm
![Page 10: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/10.jpg)
Comparison of Different System
3900mm Floor HeightFCU System
Fit-in RC
Ribbed Slab System
Fit-in Pre-stress
Flat Slab System
Fit-in Composite
Beam / Slab SystemRC
3900mm Floor Height 3900mm Floor Height
Flat Slab
2.1 MEP Services
Zone Impact
Tall Building Forum – MEP Session Guangzhou West Tower
VAV System
Underfloor AC Supply System
3900mm Floor Height4000mm Floor Height4000mm Floor Height
4000mm Floor Height 4000mm Floor Height 4000mm Floor Height
Composite Beam
![Page 11: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/11.jpg)
Headroom Summary Table
ProjectFL-FL Height (mm)
Clear Headroom
(mm)
SMEP-FL Ratio
1 Guangzhou West Tower 4500 3100 0.31
2 Shanghai China Merchant Bank 4500 3000 0.33
3 Beijing CCTV Headquaters (Main Tower) 4250 2800 0.34
4 Shenzhen Stock Exchange 4350 2900 0.33
2.1 MEP Services
Zone Impact
Tall Building Forum – MEP Session Guangzhou West Tower
5 HWP Tianjin Complex 4200 3000 0.29
6 Suzhou Gate to the East 4000 2620 0.35
7 Guangzhou R & F Mixed-Use Tower 4200 2600 0.38
8 Hong Kong Nina Tower 3850 2650 0.31
9 Chongqing World Finance Tower 4200 2800 0.33
10 Shenzhen Kingkey Finance Tower 4200 2800 0.33
Remarks: SMEP-FL denotes structural MEP zone height to floor height.
![Page 12: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/12.jpg)
Tall Building Forum – MEP Session Guangzhou West Tower
![Page 13: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/13.jpg)
• Lift core is the major element occupied the core area of tall building
2.2 Core
EfficiencyLift System
• Different lift design strategy will be considered for optimizing the core efficiency: -
� Using high speed lift
� Sky lobby
� Use of double-deck lift
Tall Building Forum – MEP Session Guangzhou West Tower
� Use of double-deck lift
![Page 14: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/14.jpg)
• Study of Grade A Office Portion
1. Conventional Option
2. Sky Lobby Option with Single-Deck Shuttle Lift
3. Sky Lobby Option with Double-Deck Shuttle Lift
Lift Traffic Analysis Comparison2.2 Core
Efficiency
Single-Deck Lift
Sky Lobby
Sky Lobby
Tall Building Forum – MEP Session Guangzhou West Tower
Double-Deck
Shuttle Lift
Single-Deck
Shuttle Lift
![Page 15: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/15.jpg)
Option 1 Option 2 Option 3
No. of Lifts 36 42 40
Lift Traffic Analysis Comparison
• Summary
2.2 Core
Efficiency
Tall Building Forum – MEP Session Guangzhou West Tower
Min. No. of
Escalators0 0 4
No. of Lift
Shafts36 24 22
Lift Shaft Volume (m3)
40,000 28,000 26,500
![Page 16: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/16.jpg)
West Tower Lift System2.2 Core
Efficiency
Sky
Local Lift
Tall Building Forum – MEP Session Guangzhou West Tower
• Double-deck shuttle lifts are applied for low and high zone on office portion of building
• 2 sky lobbies for office shuttle lifts
• 1 sky lobby for hotel shuttle lifts
• Local lifts as inter-floor transfer
Shuttle Lift
Sky Lobby
![Page 17: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/17.jpg)
Other MEP Services Inside Core
ELV
ELV
Electrical
FS
FS
Staircase Pressurization
Smoke Extraction
HVAC
PD
Floor Efficiency ~71%
2.2 Core
Efficiency
Tall Building Forum – MEP Session Guangzhou West Tower
ElectricalELV
ELV
Electrical
FS
FS
Staircase Pressurization
Smoke Extraction
Smoke Extraction
HVAC
PD
![Page 18: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/18.jpg)
Core Efficiency Summary Table2.2 Core
Efficiency
ProjectBuilding Height
(m)
Core Efficiency
(%)
1 Guangzhou West Tower 432 71
2 Shanghai China Merchant Bank 200 74
3 Beijing CCTV Headquaters (Main Tower) 234 72
4 Shenzhen Stock Exchange 240 71
Tall Building Forum – MEP Session Guangzhou West Tower
5 HWP Tianjin Complex 246 75
6 Suzhou Gate to the East 280 74
7 Guangzhou R & F Mixed-Use Tower 285 74
8 Hong Kong Nina Tower 320 72
9 Chongqing World Finance Tower 402 77
10 Shenzhen Kingkey Finance Tower 439 70
![Page 19: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/19.jpg)
Tall Building Forum – MEP Session Guangzhou West Tower
![Page 20: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/20.jpg)
• Electrical
� Power Substation (Tx room, Switchroom)
� Backup Generator
� Lift Machine Room
� Security Control Room
� Fire Services Control Room
• Mechanical
MEP Plant Space Category2.3 Ratio of TPRA
and TFA to GFA
Tall Building Forum – MEP Session Guangzhou West Tower
• Mechanical
� Chiller Plant Room
� Cooling Tower
� Potable & Flushing Water Tank and Pump
Room
� Fire Services Water Tank and Pump Room
� Smoke Extraction & Staircase Pressurization
Room
![Page 21: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/21.jpg)
Plantroom Allocation2.3 Ratio of TPRA
and TFA to GFA
Hotel ChillerAHU
Fan RoomPAUFan Room
PAU + Free Cooling FanAHUFan RoomPressurization fan & smoke extraction fan roomFS Tank
Hotel Cooling Tower
Sprinkler Water TankPotable Water TankLife Machine RoomSmoke Extraction (Atrium)PAU & AHU
Fan RoomBoiler Room
PAUAHUSmoke Extraction(Atrium)
P&D TransferAHU / Fan RoomPotable Water
Tall Building Forum – MEP Session Guangzhou West Tower
ChillerChilled Water PumpMain TX RoomGeneratorPotable WaterFS
Fan RoomLife Machine RoomSwimming Pool Filtration PlantTX Room
Fan Room
Pressurization fan & smoke extraction fan roomTX RoomPotable WaterFS Tenant Heat Rejection PAU + AHU
EAFPressurization fan & smoke extraction fan roomPotable WaterFSTX RoomHX + Chilled Water PumpTenant Heat Rejection
![Page 22: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/22.jpg)
Total Plant Space Summary Table
ProjectTFA –GFA
Ratio (%)
TPRA –GFA Ratio
(%)
1 Guangzhou West Tower 1.12 10.50
2 Shanghai China Merchant Bank 1.69 10.89 ~11%
2.3 Ratio of TPRA
and TFA to GFA
Tall Building Forum – MEP Session Guangzhou West Tower
3 Shenzhen Stock Exchange 1.66 10.46
4 Guangzhou R & F Mixed-Use Tower 1.26 10.23
5 Chongqing World Finance Tower 1.15 11.09
Remarks:
1. TFA-GFA denotes typical floor area to GFA.
2. TPRA-GFA denotes total plant room area to GFA.
![Page 23: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/23.jpg)
Tall Building Forum – MEP Session Guangzhou West Tower
![Page 24: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/24.jpg)
• Example
2.4 MEP System
for Composite
Building
Architectural Zoning
Zone A: Executive
Office
Zone B: Hotel
Tall Building Forum – MEP Session Guangzhou West Tower
Zone C: Office
Zone E: Car Park
Zone D: Retail
![Page 25: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/25.jpg)
• LV Power Distribution System
MEP Functional Zoning
Zone A: Executive
Office Zone B: Hotel
Zone AZone B
2.4 MEP System
for Composite
Building
Tall Building Forum – MEP Session Guangzhou West Tower
Architectural Zoning
Zone C: Office
Zone E: Car Park
MEP Zoning
Zone C
Zone DZone D: Retail
![Page 26: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/26.jpg)
• HVAC System
MEP Functional Zoning
Zone A: Executive
Office Zone B: Hotel
Zone BZone A
2.4 MEP System
for Composite
Building
Tall Building Forum – MEP Session Guangzhou West Tower
Architectural Zoning
Zone C: Office
Zone E: Car Park
Zone D: Retail
MEP Zoning
Zone C
![Page 27: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/27.jpg)
• Lift System
MEP Functional Zoning
Zone A: Executive
Office Zone B: Hotel
Zone BZone A
2.4 MEP System
for Composite
Building
Tall Building Forum – MEP Session Guangzhou West Tower
Architectural Zoning
Zone C: Office
Zone E: Car Park
MEP Zoning
Zone C
Zone D
Zone E
Zone D: Retail
![Page 28: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/28.jpg)
2.4 MEP System
for Composite
Building
West Tower Zoning Arrangement
Zone 3: Office
Zone 4: Hotel
Refuge / ME 4
Zone 3: Hotel
Zone 2: OfficeRefuge
ME5
Tall Building Forum – MEP Session Guangzhou West Tower
MEP Zoning for LV DistributionArchitectural Zoning
Zone 1: Suite Office,
Podium, Carpark
Zone 2: Basement
Chiller Plant
Zone 1: Retails,
Basement, Carpark
Refuge / ME 1
Refuge / ME 2
Refuge / ME 3
![Page 29: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/29.jpg)
Tall Building Forum – MEP Session Guangzhou West Tower
![Page 30: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/30.jpg)
2.5 Centralized vs
De-centralized
System
• For super tall building, composite zoning is normally adopted
• Centralized System
� Fire Services System
� Plumbing System
� Security System
System Arrangement
Tall Building Forum – MEP Session Guangzhou West Tower
• De-centralized System
� Air-conditioning System
� Power Supply System
� Lift System
![Page 31: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/31.jpg)
2.5 Centralized vs
De-centralized
System
Centralized AHU System
• Located at one or more specified floors
Pros: -
• No AHU at typical floor - increase core efficiency of typical floor
• Centralized maintenance works
Tall Building Forum – MEP Session Guangzhou West Tower
• Centralized maintenance works
Cons: -
• More plant space requires at podium area and main entrance floor
• Duct-borne noise is existed
![Page 32: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/32.jpg)
2.5 Centralized vs
De-centralized
System
De-centralized AHU System
• Located at each typical floor
Pros: -
• Better individual AC control
• High availability for equipment selection
• Less plant space required at
Tall Building Forum – MEP Session Guangzhou West Tower
• Less plant space required at podium area and main entrance floor
Cons: -
• Reduce core efficiency of typical floor
• More individual maintenance work
![Page 33: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/33.jpg)
2.5 Centralized vs
De-centralized
System
West Tower AHU System
AHU on each floor
AHU on each floor
Tall Building Forum – MEP Session Guangzhou West Tower
De-centralized AHU System in GZ West Tower
![Page 34: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/34.jpg)
Tall Building Forum – MEP Session Guangzhou West Tower
Summary
![Page 35: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/35.jpg)
MEP Design Considerations for Tall Buildings
- MEP Services Zone Impact on Floor-to-floor height
- Core Efficiency
- Ratio of Total Plant Room Area (TPRA) and Typical Floor Area (TFA)
3.0 Summary
Tall Building Forum – MEP Session Guangzhou West Tower
- Ratio of Total Plant Room Area (TPRA) and Typical Floor Area (TFA)
to Gross Floor Area (GFA)
- MEP System for Composite Building
- Centralized vs De-centralized System
![Page 36: 2008-11-17 Tall Building Forum - MEP Session (GZ West Tower)](https://reader034.vdocuments.us/reader034/viewer/2022051314/553d333b550346bf358b4572/html5/thumbnails/36.jpg)
Tall Building Forum – MEP Session Guangzhou West Tower