2003 ibc allowable floor area check from forum engineer web site

Upload: livian-teddy

Post on 14-Apr-2018

215 views

Category:

Documents


0 download

TRANSCRIPT

  • 7/29/2019 2003 IBC Allowable Floor Area Check From Forum Engineer Web Site

    1/3

    SECTION 507 UNLIMITED AREA BUILDINGS

    Go to the next TAB and calculate floor area.YES #

    NO #

    YES #

    NO #

    YES #

    NO #

    The above-mentioned 60' frontage may be reduced to not less than 40', provided:

    1. The reduced frontage is not more than 75% of the building perimeter.

    2. Exterior walls facing the reduced frontage have a min. fire-resistance rating of 3 hr.

    3. Openings in the above-mentioned walls are protected to 3-hr rating.

    YES #

    NO #

    1. Used as a church, community hall, dance hall, exhibition hall, gymnasium,

    lecture hall, indoor swimming pool or tennis court.

    2. The building has no stage other than a platform.

    3. The assembly floor is located within 21" of street or grade level and all exits are

    provided with ramps complying with Section 1010.1 to the street or grade level.

    Group H-2, H-3, and H-4 fire areas are permitted in unlimited area buildings having

    occupancies in Groups F and S, provided:

    1. Fire areas around building perimeter not exceed 10% of the building area nor

    the area determined by Table 503 plus the frontage increase in Section 506.2

    One-story, sprinklered throughout, Group A-3 building of Type I or II construction

    surrounded and adjoined by 60' public ways or yards, provided:

    Section 507.4

    Section 507.5

    Section 507.6

    One-story Group F-2 or S-2 building surrounded and adjoined by 60' public ways or

    yardsSection 507.1

    One- or two-story, sprinklered throughout, Group B, F, M, or S building surrounded and

    adjoined by 60' public ways or yardsSections 507.2 & 507.3

    One-story, sprinklered throughout, Group A-4 building of other than Type V construction

    surrounded and adjoined by 60' public ways or yards Section 507.2

  • 7/29/2019 2003 IBC Allowable Floor Area Check From Forum Engineer Web Site

    2/3

    Project:Developed by Mark Chang

    Separated Uses? YES -- Section 302.3.1 vs Section 302.3.2 Version 2.0

    Number of Stories: 2 Number of Frontage Cases: 3 Number of Occupancy Groups: 3

    FALSE -- Qualify UL area per Section 507.1, 507.2, 507.3, 507.5, 507.8, or 507.9 except the 60' frontage requirement.

    NO -- The building in consideration is a 4-story, R-occupancy, and sprkinklered per NFPA 13R throughout.

    F (in feet) = Length of the exterior walls facing the associated frontage

    P (in feet) = Perimeter of the building = Length of the total exterior walls

    Fron tage Case 1: Fron tage Case 2: Frontage Case 3:

    Width of Frontage (in feet) = 30 Width of Frontage (in feet) = 20 Width of Frontage (in feet) = 28

    F = 405 F = 710 F = 650

    P = 810 P = 810 P = 810

    F / P = 0.500 F / P = 0.877 F / P = 0.802

    If = 100 (F/P-0.25) (W/30) = 25.0 If = 100 (F/P-0.25) (W/30) = 41.8 If = 100 (F/P-0.25) (W/30) = 51.6

    Floor Number: 1

    Occupancy Group 1: B Occupancy Group 2: F-1 Occupancy Group 3: S-2

    Type of Construction: Type V-B Type of Construction: Type V-B Type of Construction: Type V-B

    Sprinkler Throughout? NO Sprinkler Throughout? NO Sprinkler Throughout? NO

    Sprinkler for Fire-Rating Sub? NO Sprinkler for Fire-Rating Sub? NO Sprinkler for Fire-Rating Sub? NO

    Actual Floor Area (A1): 6,000 Actual Floor Area (A2): 4,800 Actual Floor Area (A3): 3,600Tabular Area per Floor (At): 9,000 Tabular Area per Floor (At): 8,500 Tabular Area per Floor (At): 13,500

    Frontage Increase (At If / 100): 4,641 ### Frontage Increase (At If / 100): 4,383 Frontage Increase (At If / 100): 6,961 ##

    Sprinkler Increase (At Is / 100): 0 Sprinkler Increase (At Is / 100): 0 Sprinkler Increase (At Is / 100): 0 1.

    Allowable Area per Floor (Aa1): 13,641 0.4 Allowable Area per Floor (Aa2): 12,883 Allowable Area per Floor (Aa3): 20,461 0.

    Tabular All. Number of Stories: 2 Tabular All. Number of Stories: 1 Tabular All. Number of Stories: 2

    2 14569

    A1/Aa1 + A2/Aa2 + A3/Aa3 = 0.99 (OK) Maximum Area (sq.ft.) of The Building = 29,138

    1

    On The Dou ble, Inc .

    0

    1

    ##

  • 7/29/2019 2003 IBC Allowable Floor Area Check From Forum Engineer Web Site

    3/3

    302.3.1 Nonseparated uses. Each portion of the building

    shall be individually classified as to use. The required type

    of construction for the building shall be determined by applying

    the height and area limitations for each of the applicable

    occupancies to the entire building. The mostrestrictive type of construction, so determined, shall apply

    to the entire building. All other code requirements shall apply

    to each portion of the building based on the use of that

    space except that the most restrictive applicable provisions

    of Section 403 and Chapter 9 shall apply to these SECTION 403 HIGH-RISE BUILDINGS

    nonseparated uses. Fire separations are not required between CHAPTER 9 FIRE PROTECTION SYSTEMS

    uses, except as required by other provisions.

    302.3.2 Separated uses. Each portion of the building shall

    be individually classified as to use and shall be completely

    separated from adjacent areas by fire barrier walls or horizontal

    assemblies or both having a fire-resistance rating determined

    in accordance with Table 302.3.2 for uses being

    separated. Each fire area shall comply with this code based

    on the use of that space. Each fire area shall comply with the

    height limitations based on the use of that space and the type

    of construction classification. In each story, the building

    area shall be such that the sum of the ratios of the floor area

    of each use divided by the allowable area for each use shallnot exceed one.